Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Wet vent vs hack up wall studs more
Author: kolky (MO)

I am turning my previous kitchen into a mud room and adding a washer and dryer. I'm running into a few issues figuring out how to run the plumbing and could use some advice.

Here is a picture of how the sink was previously plumbed.



Here are the issues I'm having.

- The plumbing is on an exterior wall farmed with 2x4s.
- The stud cavity that main line / vent is in is small
- The way the sink was previously plumbed took some major notches out of the studs already

My plan is to run 2" PVC up from the basement below. I then plan to build a wall out vertically from this wall to house the standpipe and p-trap for the washing machine to keep it from freezing.

I would like to do something like this with the washing machine trap facing forward instead of to the side.



Unfortunately as you can see in the first picture this will require me to hack up the king stud of the window even more that it already is.

The image below would also be an option. I realize it's a wet vent but I could use the existing notches and that seems better than hacking another hole in the 2x4s.




Any thoughts on what my best approach would be? Fixture venting the washer line doesn't seem like it will work either because due to space I need to keep the stand pipe close to the exterior wall. It also seems like the current layout with the dual drains was already wet vented anyway?



Edited 1 times.

Post Reply

 Re: Wet vent vs hack up wall studs more
Author: packy (MA)

keep your laundry trap full size 2 inch and you should be fine..

Post Reply

 Packy, thanks for the reply cool
Author: kolky (MO)

Packy, thanks for the reply. I'm assuming you mean I should be fine wet venting the utility sink assuming that I keep the washer drain and p-trap 2"? That was my plan even though the third image shows 1 1/2".



Edited 2 times.

Post Reply

 Re: Wet vent vs hack up wall studs more
Author: packy (MA)

you are wet venting the laundry with the utility sink. so, as long as the vent remains full size 2 inch an the san tees are closer than 10 inches apart, you are good to go.
you need a cleanout in there as well. above the top of the washing machine (in the vent ) is fine..

Post Reply

 Re: Wet vent vs hack up wall studs more
Author: North Carolina Plumber (NC)

The tee for the sink needs to be above the tee for the washer drain trap. The stand pipe out of the trap needs to be at least 24" tall ( 2015 UPC Code ). The opening into the standpipe needs to be at least 35" from the floor.

Post Reply

 24" ?
Author: steve (CA)

804.1 of the 2015 UPC states standpipe shall be 18" to 30".

Post Reply

 Re: Wet vent vs hack up wall studs more
Author: kolky (MO)

Packy,

Regarding the cleanout. If I have one directly below these drains in the basement is that sufficient or do I need to have one on this floor as well?

Post Reply

 Re: Wet vent vs hack up wall studs more
Author: srloren (CA)

I would put a clean out in because these are two of the most likely drains in the house to get clogged IMHO. Also, the photo may lie but make sure you have grade on those horizontal lines to the trap if you plumb it that way. Copper is smoother than Cast Iron and a little less likely to build up debris...a little.



Edited 1 times.

Post Reply

 Re: Wet vent vs hack up wall studs more
Author: packy (MA)

cleanout below covers the code.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.