Over 698,000 strictly plumbing related posts
Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
jeffasweet (CA)
Hi All,
Water heater is in unfinished basement without a drain. Inspector gave me a diagram that uses a tee and drains the valve outside but a 1/4" copper loop right below the heater, which he said to crimp almost closed at the end. My understanding is this lets you see if your valve is dripping but if it blows, then water will flow to the outside.
I've run the drain outside, went to rafters with galvanized then transitioned to Pex for the remainder of the run, to keep Pex 18" away from the heater. I plan on running the pex into a dry well that I have to dig.
Is this going to work?
Here's the diagram the inspector gave me (I'm in San Jose, CA).
Also, Packy, I'm close to getting the plumbing finished finally including the recirculating line you advised me on.
Thanks Jeff
Edited 3 times.
|
Post Reply
|
Author:
bernabeu (SC)
work - yes
code compliant - evidently
best practice - no way
my opinion: leave the basement unfinished and terminate the 'blow off' 6" above floor with a water alarm/shut off device
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
packy (MA)
to quote grouch marks, that's the most rediculous thing i have ever heard...
|
Post Reply
|
Author:
packy (MA)
my code says 9-12 inches off floor. enough to get a bucket under it..
|
Post Reply
|
Author:
North Carolina Plumber (NC)
We have to pipe the T + P within 6" of the floor here. I always put a floor drain near where the water heater is going to be when doing the underslab work.
I can honestly say I have never saw a T + P valve piped like in that picture.
|
Post Reply
|
Author:
hj (AZ)
I used to have an agreement with the head plumbing inspector so I could do that, but when he retired his successor said "no way", so I am surprised that an inspector even knows how to do it, much less recommend it. The "drip" from the 1/4" line is to drain the overhead portion, (and if the end outside is lower than the end of the 1/4", it will siphon itself with only a small amount of water leaking from the 1/4"
|
Post Reply
|
Author:
PlumerDan (CA)
Hj,I put a water heater in the basement of mayor of San Jose so I had the chief inspector make me do the same thing...remember the code is open to interpratation
|
Post Reply
|
Author:
jeffasweet (CA)
Thanks for the feedback. At least I know I'm not the only one who has had to do it and thinks it's crazy. Now I just need to find someone to dig a 2'x2'x2' dry well to drain into.
Jeff
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|