Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 residential water pressure.
Author: jritch (PA)

I have city water with a pressure regulator set at 70 psi. When a toilet is flushed, a pressure gauge shows that the pressure drops from 70 psi to 20 psi. If another fixture is opened while the toilet tank is filling, the gauge drops to 10 psi. My question is, would a booster pump system of some kind help to keep a more uniform pressure or flow, in the water lines, when multiple fixtures are open at the same time. For instance, could two showers be open at the same time without signigicant loss of pressure with a booster system added. The water line coming into the house is 3/4, but drops to 1/2 inch coming out of the pressure regulator and continuing throughout the house. Thanks for any help or answers to my question.

Post Reply

 Re: residential water pressure.
Author: packy (MA)

first check that there is a fliter screen at the inlet of the PRV and that it is clean.

Post Reply

 Re: residential water pressure.
Author: jritch (PA)

Thanks for the reply Packy. The PRV is new. My old one just went bad and was causing me problems with TP valve going off on the water heater and putting water on the floor. I think the old PRV was going bad for a while, so we had gotten used to higher pressure coming in to the house. With new PRV, we now notice a big change in pressure, when a couple of fixtures are open at the same time.

Post Reply

 Re: residential water pressure.
Author: packy (MA)

still check for debris in a filter screen. could have happened when the water was turned back on after install.

Post Reply

 Re: residential water pressure.
Author: jritch (PA)

So you are saying that the drop in pressure I have described, is not a normal situation? I will check for debris. Thanks.

Post Reply

 Re: residential water pressure.
Author: packy (MA)

i have seen plenty of houses with only a single 1/2 inch water main.
there is no large pressure drop when a single fixture is used.
my guess is a restriction somewhere which leads me to believe a clogged screen at the PRV.
of course i could be all wet on this.

Post Reply

 Re: residential water pressure.
Author: hj (AZ)

Your regulator is "defective". Change it, and your problems will go away.



Edited 1 times.

Post Reply

 Re: residential water pressure.
Author: jritch (PA)

There was no debris found in the the regulator. So HJ, with the piping I described and the drop in pressures that I observed, what would you expect the pressure to drop to on the gauge, with a properly working regulator, and one fixture open? Then, with two fixtures open? Thanks.

Post Reply

 Re: residential water pressure.
Author: hj (AZ)

A 5 psi drop would be a lot with a properly functioning PRV. And the amount of drop would depend on the flow rate of the faucet. In most cases, the drop would be almost imperceptable.

Post Reply

 Thanks so much for your help. smile
Author: jritch (PA)

Packy and HJ. Replaced regulator with another new one and pressure has increased significantly. First new one must have been defective as you guys suggested. Water pressure now starts at 70 psi and with two fixtures open, it drops to about 50 psi. Much more acceptable. Thanks so much for your help.



Edited 1 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.