Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
takane (NY)
I installed a new lowboy hot water heater under the counter. Unfortunately the pressure relief valve was on top of the tank and I did not have enough clearance.
I installed a brass close nipple and elbow and another brass nipple and installed the pressure relief valve horizontally.
Is this OK? I don't see any reason why this would not work, even though it's not hooked up directly to the tank.
Thank you
|
Post Reply
|
Author:
packy (MA)
it is in the wrong place. it will sense pressure but not temperature.
|
Post Reply
|
Author:
bernabeu (SC)
POTENTIALLY LETHAL SAFETY HAZARD
ABSOLUTELY POSITIVELY WRONG AND UNSAFE
The 'relief valve' for a water heater is a TEMPERATURE and PRESSURE relief !
relieves at 210 degree F. OR 150 psi (some tanks will have 210/125)
By mounting it 'remote' and horizontal you have removed the temperature sensitive rod from DIRECT IMMERSION in the heater AND lowered/voided the btu per hour rating of the valve assembly.
the white 'probe' is what senses temperature - it MUST be FULLY IMMERSED in the BODY of the water heater - repeat: FULLY IMMERSED in the BODY of the heater
If the heater you bought does not fit the space, you will need to get one which does fit without any modification to the TPSRV (temperature-pressure safety relief valve which is ABSOLUTELY REQUIRED to be PROPERLY installed.
ps. there are 'some' models of water heater with the TPSRV directly mounted in the side (all the way up, of course)
pps. your insurance will NOT cover your damages if the heater fails and subsequently explodes due to your modification which rendered the TEMPERATURE relief inoperative or ineffective
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
packy,
imo: a major issue is the reduction in effective discharge BTU capacity as well as the reduction and serious lag in 'temperature sensitivity/reaction time'
I am sure you will concur that the OP's action is DANGEROUS and needs IMMEDIATE correction !
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 2 times.
|
Post Reply
|
Author:
packy (MA)
hold onto your hat, my friend from SC... I concur....
|
Post Reply
|
Author:
bernabeu (SC)
O ~ M ~ G
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
hj (AZ)
How many reasons do you want for it to be illegal. What you have done is converted a T&P safety valve into "P" safety valve.
|
Post Reply
|
Author:
hj (AZ)
The flow reduction would be minimal, but the temperature lag would be "infinite" because it will NEVER sense the actual temperature inside the tank.
|
Post Reply
|
Author:
m & m (MD)
Do a search on water heater explosions during the last part of the 19th century and early 20th century and how a simple, properly installed T&P valve virtually eliminated these disasters.
|
Post Reply
|
Author:
hj (AZ)
There are plenty in the early 21st century if they cannot find the ones from the 20th century.
|
Post Reply
|
Author:
takane (NY)
Wow! Didn't think about the
temperature. I will correct
it right away.
Thanks for the response.
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|