Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
doug_mb (Non-US)
The sump pump that came with my new home failed after 10 years. I thought it would be an easy thing to replace - apparently not. I have bought two new pumps because I thought the first one I bought was faulty but I have the same problem with the second.
The original sump pump did not have a check valve and never got air locked. It ran problem-free. The new pump gets air locked all the time. I have tried installing a check valve in the pit above the pump and when that didn't work I tried installing a valve where the pump rises up the basement wall to exit the house. I have also tried drilling a hole in the pipe in the pit. Nothing works.
I am thinking that the design of the discharge pipe contributes to the problem because it seems to me that it has a built in air trap. The pipe comes out of the pit, rises about 6 inches above the basement floor, and then runs horizontal for about a foot. The pipe then runs back down through the basement floor and runs under the concrete slab all the way to the other side of the basement where it rises out of the floor, runs up the wall and out of the house. Water probably gets trapped in the pipe under the slab and there is air trapped in that horizontal one foot long part above the sump pit.
Any ideas as to what the problem is and what I need to do?
|
Post Reply
|
Author:
jerco (MD)
Sounds like the discharge line is clogged up.
|
Post Reply
|
Author:
packy (MA)
drill a 3/16 hole in the pipe below the check valve. drill the hole at an angle upwards so the water will spray downwards.
Edited 1 times.
|
Post Reply
|
Author:
LemonPlumber (FL)
think Packy has you covered.
|
Post Reply
|
Author:
doug_mb (Non-US)
Thanks for the responses. I don't think the discharge line is blocked as it works fine once I get the air out of the system (until) the next time).
I don't currently have a check valve as the old sump pump worked fine without one. I did try putting one in though and I did drill a hole below as you suggest. It didn't help - so I took the check valve (and hole) out.
|
Post Reply
|
Author:
LemonPlumber (FL)
Doug is this pit sealed?Is it vented after the cover goes on?
|
Post Reply
|
Author:
doug_mb (Non-US)
The pit used to be sealed but I damaged the cover when I replaced the original pump (had to cut it off) so it is no longer sealed. Would it make a difference in the operation of the pump if the pit were sealed?
|
Post Reply
|
Author:
SMSPlumbing (MD)
It sounds to me that something is in your discharge line. Your other pump did not have a check valve because the way you explained the pipe sounds like it makes a trap. I would snake the line out regardless you may think it is fine. I would still leave the hole in the pipe whether you have the check valve or not.
|
Post Reply
|
Author:
hj (AZ)
An "air trap" ONLY occurs inside the pump, and a properly drilled hole in the riser pipe eliminates that. You have a completely different problem, but it is NOT an air lock, from what you have described and what you say you have done already.
|
Post Reply
|
Author:
hj (AZ)
HOW do you get the air out "until the next time"?
|
Post Reply
|
Author:
doug_mb (Non-US)
To remove the original pump after it failed, I had to cut the discharge line and I did that at that one foot horizontal area above the pit. When I installed the new pump I used one of those rubber connectors with the two hose clamps. To get the air out, when the pump is running I loosen off one of the clamps and air comes rushing out. When it starts to spit out water I unplug the pump and tighten the clamp. When I unplug the pump you can hear water falling back down into the pit.
I then plug the pump back in and it usually works. Sometimes though I need to do this a couple of times.
It is like there is water in the pipe under the slab and air in the pipe in the horizontal part above the slab - and in order to actually pump out water that air as to be removed. That horizontal part works just like a trap under a sink only it traps air (because it is like an "N" instead of a "U" instead of water like a sink trap.
|
Post Reply
|
Author:
SMSPlumbing (MD)
Is there a reason you have to keep the same pipe set up? Can you go straight above the pit then out?
|
Post Reply
|
Author:
doug_mb (Non-US)
I would like to keep the same setup if possible as my basement is finished as living space and it would require extensive renovation to change the location of the discharge pipe.
|
Post Reply
|
Author:
treeman8 (MI)
Could the current system have a huge amount of head pressure with the water sitting in the pipe under the slab?
Did the old pump have some design that had a check valve right at the pump so that little or no air ever entered the pump? EDIT TO READ "no air entered the LINE (not pump)"
Could a few feet of air in the line near the pump be enough of a compressive cushion so that the pump cannot overcome the large head pressure?
Is your new pump maybe too wimpy or of a different design to overcome the hypothetical head pressure?
Just some guesses on an intriguing problem.
Edited 2 times.
|
Post Reply
|
Author:
hj (AZ)
The pump creates "pressure" which will push any air out of the line. It is more likely that you are venting the air from the pump so it CAN create the pressure.
|
Post Reply
|
Author:
doug_mb (Non-US)
>>Is your new pump maybe too wimpy or of a different design to overcome the hypothetical head >>pressure?
No. The old sump pump was a 1/4 HP and the one I am currently using is of the same design and 1/2 HP. I had also tried one of a different design and 3/4 HP.
>>The pump creates "pressure" which will push any air out of the line. It is more likely that you >>are venting the air from the pump so it CAN create the pressure.
How does this air get in the pump? How would I prevent this?
|
Post Reply
|
Author:
LemonPlumber (FL)
If you drilled a hole just above the water level at activation it should have worked as said.check /trap or none.
|
Post Reply
|
Author:
doug_mb (Non-US)
I will try that again. Perhaps when I drilled a hole before it was too high or too low...
|
Post Reply
|
Author:
LemonPlumber (FL)
It needs only be above the water line when the pump starts.drilling upward so it sprays downward is smart.but the hole lets air out and will also spray out water when the pump is pumping water.
|
Post Reply
|
Author:
hj (AZ)
ONe way is if the pump does not turn off when all the water is out of the pit. In fact, it is about the only way it can happen.
|
Post Reply
|
Author:
doug_mb (Non-US)
The hole has been drilled. I will monitor the situation and report back. Thanks for all your help.
|
Post Reply
|
Author:
hj (AZ)
IF it works, then find out WHY it was getting air into the pump, because that only happens when there is a malfunction of the float.
|
Post Reply
|
Author:
doug_mb (Non-US)
So far I am still having the problem. The only difference now is that water shoots out of the hole (at great pressure) but still doesn't go up and out the discharge pipe until I unplug the power cord a couple of times. When I do that there is some gurgling in the pipe and when I plug the cord back in - it will discharge.
|
Post Reply
|
Author:
hj (AZ)
YOu have a problem which may be impossible to diagnose without being there. IF water is coming out of the hole then the pump is creating pressure, and as long as there is pressure, ANYTHING in the pipe should be pushed out, and if cannot be pushed out, the water should not flow no matter how many times you plug the pump in.
|
Post Reply
|
Author:
LemonPlumber (FL)
Are yous sure it would not empty the pit in time or have you set the amount of time by the running time?The top third of the lift station may take longer with some activation set up,s?Is the inlet covered with water before the pump starts?
|
Post Reply
|
Author:
doug_mb (Non-US)
When the pump stops after pumping water out of the pit there is still about 6 inches of water left in the pit - so the inlet is covered.
I am trying something else here. I have shortened the discharge hose in the yard to just a few feet so it completely drains after the sump pump is finished. There will still be water left in the pipe that runs under the basement slab but perhaps water standing in the hose outside adds to the problem.
|
Post Reply
|
Author:
LemonPlumber (FL)
I have installed many pits that have a thousand or more gallons of water in the lines before the pump starts.when the pump does start does the water flow out the relief hole ?It means the pump is pumping.this may be a point.I am missing other wise.
|
Post Reply
|
Author:
doug_mb (Non-US)
Yes. When the pump starts the water flows out of the relief hole with lots of pressure. When the pump stops, there is not a lot of water that comes out of the relief hole. Probably just from the couple of feet of pipe before the pipe goes horizontal. I was thinking that perhaps all of the water in rest of the pipe and the hose outside the house was acting like a vacuum - preventing more water from falling back down. That was the reason I shortened the hose outside.
|
Post Reply
|
Author:
LemonPlumber (FL)
Hose is 1 1/4" ?you seem to be asking if you have a lessor pump.buy a really large hose!!!king if a straw will empty a glass quickly.
|
Post Reply
|
Author:
doug_mb (Non-US)
Yeah, the hose outside is small - 1 1/4 or 1 1/2. That seems to all Home Depot ever sells (right now they have absolutely none in stock).
|
Post Reply
|
Author:
SMSPlumbing (MD)
You do not want the whole pipe to drain back into the pit or the pump will just cycle that water. If the pipe just there at the pump drains back, that is fine.
Depending on where your float is set, that will depict where the water level will be when the pump shuts off. And then add the foot or so of water that drains back.
To me it sounds as if there is a blockage still somewhere in the pipe.
|
Post Reply
|
Author:
hj (AZ)
You are "grasping at straws" and have no idea what the problem is, and thus no way to determine how to fix it. Your description of the symptoms, as Spock would say, is "illogical", and therefore we can't help either.
|
Post Reply
|
Author:
hj (AZ)
That also has absolutely nothing to do with your problem. One possibility, and I would have to be there to see the actual installation, would be if the piping is arranged so it can "siphon" the water out of the pit once the pump starts. That could be the reason that very little water drains back when the pump stops. BUT, it would also NOT prevent the pump from removing the water when it starts.
|
Post Reply
|
Author:
mrmac (TX)
You might try an automatic air vent on the horizontal line, the kind used on chilled and heating water systems. You can valve it on the bottom and run the discharge line back to the sump pit. Maybe put a tee in with a 1/4 " valve to eliminate air and see if it helps before you buy the aav. Most commercial supply houses have them.
|
Post Reply
|
Author:
doug_mb (Non-US)
New information.
The pump is still not working properly although water shoots out of the 3/16 inch hole just wonderfully. Tonight I had to turn the pump off and on a couple of times to try and get it working. The first time I turned it off there was lots of gurgling from inside the discharge line and was water fell back into the pit there were also some air bubbles coming out.
The pump still would not work so I did what I have done numerous times before - with the pump running, I loosened off the clamp where the discharge line is joined in the horizontal area above the pit(where I cut it to remove the original pump). This causes air to rush out of the joint under pressure. When water starts spitting out instead of air I tighten the clamp and turn off the pump. When I turn the pump back on again it pumps just fine.
When it finishes its job a bit of water falls back into the pit and some air bubbles too.
The pump always spits water out of the 3/16 inch hole with good pressure but it can't seem to get by air trapped in the line until I bleed the air out. I have flushed out the line by inserting a hose outside the house and it runs freely down into the pit so there does not seem to be a blockage.
Any ideas as to how this air accumulates in the line in the horizontal area? Someone mentioned in an earlier post that this should not stop the pump from discharging the water but it certainly seems to.
|
Post Reply
|
Author:
jerco (MD)
I think it's safe to say that we are as baffled as you are. Air lock should only occur at the pump. If water is spraying out of the hole then the air lock is solved and water should push all the way through the line regardless of additional air pockets along the way. I don't know what to tell you.
|
Post Reply
|
Author:
fishEH (IL)
Sounds like your check valve in installed backwards. You shouldn't be able to run a garden hose at the discharge end and have the water come into your sump pit.
|
Post Reply
|
Author:
rickster (NY)
Here's where I think the problem lies.
Your pipe comes UP out of the sump pit, goes horiz, then goes BACK DOWN and under the slab. That turn >> DOWN is the problem.
In that DOWN segment, right after the pump cycles off, the falling of that last volume of water downward sucks air into the line because the pump has stopped delivering water into the pipe. An air pocket forms in that vertical section of pipe. THen the pump cycles on again and that air bubble gets pushed along. And then the next few cycles adds to the ammount of air. And voila! Soon, you have an air lock in the piping. This air can't escape through your relief hole because it is drilled upstream of this segment of piping.
Solutions?
(1) Not easy: Put an air relief hole downstream of that DOWN segment of pipe.
(2) More reaonable:
Run your pipe directly from the sump pump up so many inches, then one 90-degree turn towards the horizontal run of pipe under the slab. ( No upsies and downsies and upsies! ) So that means a little concrete demolition. (Rent a heavy duty Masonry drill with jackhammer feature at Home Depot. Drill holes then switch to jack hammer mode to break it up. )
I can't guarantee this is the problem, but it is a good possibility.
|
Post Reply
|
Author:
Sense2k (NJ)
Hello
I just joined. I have the exact same problem.
Doug, did you find out exactly what causes this?
Did you find a solution?
i will try to do same thing - disconnect hose at check valve to let air out etc
|
Post Reply
|
Author:
doug_mb (Non-US)
I still have the problem which I believe is probably caused by the discharge line which runs under the concrete floor being bowed up (due to the house settling). I deal with it by putting the sump pump on a timer which will allow the pump to run for 30 minutes and then shut off a few times a day. If the pump is not really pumping and the pit is not being emptied the water (and air) that is in the discharge line will then run back into the pit. This clears the air lock in the line without my having to be there and the pump will work properly the next time the timer allows the pump to start.
Still do not know why this issue only started after the initial pump failed.
|
Post Reply
|
Author:
Eric Window2 (NC)
OK I have the same problem. I used the same piping and same type pump when I replaced it. My old pump went out because the seal leaked. I have checked the hole is drilled and not clogged. My pump runs, but does not pump water unless I unplug it and replug it. It doesn't happen all the time, just most of the time. Only thing different I can tell is the float switch may be a bit higher than before because my old pump seemed to cycle to much. This is a sewage sump pump made by Zoeller. My water drains just fine when the pump works and some water returns to the tank after it shuts off. Anybody figured this out.
|
Post Reply
|
Author:
Zurk (OH)
You need to get the net head pressure needed (NPSH) in your system to get the correct solution. From what you've said this was pretty much a closed/primed system before the pumping failed and when you opened it up all of the "mysterious" check-valve, air pocket, pump cavitation issues popped up without checking it while it was running OK, ALL of them may have failed all at once. The hidden critter is the vertical DROP after the initial 6 inch up from the pump floor (how far down is the bottom of the pump to the very top of the discharge outlet using a simple yard stick...), there can be air getting into the system holding up pumpage anywhere, even a check valve seal -- Add up all of the vertical inches UP from the floor of the sump to the TOP of the discharge outlet, subtract all of vertical inches DOWN in the system, allow for the length of the run to size the pump, and AFTER you get this particular puppy up and running, save your notes and Buy an Extra Set of Everything for the next time bec there will be another one in that old house.
|
Post Reply
|
Author:
KevinD (IL)
I'm not sure how old this post is, but having a very similar issue. Bought a Basement Watchdog 3/4hp pump, dropped it in a well with check valve and weep hole drilled into PVC as per spec. First run worked like a champ, however the float switch kept the pump running for about 3 seconds longer than needed. That is, the pump was running with very little water in the well and it sucked in some air. Next run, the pump hummed, but no water was expelled for about thirty seconds. It was like the pump was trying to prime itself with water. It finally got its legs and ejected the water from the well, but again ran 3 secs too long and then the next run was the same issue.
Took the pump back to the store and swapped it out for another. Same install, same results. Then tried an experiment. Took the switch away and manually plugged in the pump to simulate switch "on" but unplugged pump just before well was empty enough for pump to suck in air. Let well refill with water and simulated switch "on" again. Works! Repeated. Worked again. And again. So it's clear that the pump cannot run until well is dry. But the switch is hard-coded to run for 10 seconds, which is 3 seconds too long.
Seems like a design flaw in the pump. Is there a workaround?
|
Post Reply
|
Author:
Phil-18 (PA)
I have same problem, so what I did I take check valve out and let water run back to the sump pit then it run ok , my old sump pump do not have check valve, and when I replace new one and I add the check valve, the problem start, I drill hole 1/8 Dia. it not work, then drill open to 3/16 dia. still not work, pump run and no discharge water thru the discharge pipe, I unplug then start the backup battery pump run for 15 second then plug the sump pump back in the it work ( backup pump run same discharge pipe), I noted before float switch turn of the pump it swirl in the sump pit I think it start get air go in to the pump, when water a rise it run but no water pushing thru the discharge pipe, it need help from battery back up pump, so I decide to take the check valve out and it working fine, I will put check valve back when I have other pump just order yesterday, this pump build in Anti-Airlock and do not need drill the hole to release air trap in side pump.
Edited 1 times.
|
Post Reply
|
Author:
oldyellr (Canada)
I just ran into a similar problem and solved it (for now).
I've had this Simer 1/2 HP submersible cast iron sump for about 7 years and it's always worked perfectly. Today after a heavy deluge I heard my high water alarm because the water level was up around 8" below the floor. The pump was humming, but couldn't hear water going up the pipe. I unplugged it for a while in case it had overheated or something, but when I plugged it in again, same thing. So I started unscrewing the upper check valve connection, about 2' above the floor and water came out. When that was drained, I tightened it back up. I then plugged the pump back in and lo and behold it pumped out the sump in short order and has been working fine ever since. So what happened? Had the sump filled up so quickly during the deluge that the pump could not pump against about 10' head? Or had it sat dry so long before that the rotor was air locked? I found the pump manual and there's something about drilling a 1/8" hole in the discharge pipe just above where it screws into the pump and I can't remember if I did that when I installed it. But a couple of months ago when we had a long period of constant rain I thought the pump was cycling too frequently and noticed a lot of water squirting out around the threaded connection and recirculating, so I wrapped it with silicone tape and it cycled less frequently. So maybe I covered that hole? I'll probably have to replace that connection this summer when we're out of the rainy season.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|