Plbg.com (aka: PlumbingForum.com) where plumbing help, advice, education, information, and plumbing related suggestions are provided FREE by some of the most experienced plumbing contractors and plumbers anywhere who all wish to "give back" to society. Since 1996 we have been completely free of popup advertising or any other invasive ads and have been known to be the best online STRICTLY PLUMBING advice and help site. You've come to the right place IF you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. We absolutely do not sell your personal information. We are made possible by:
|
Author:
steve (CA)
If you were in the US and there are fixtures draining into that vertical pipe from above storeys, then that standpipe would not be allowed without adding a vent between the trap and in-wall pipe. Canada does allow wet venting multiple storeys into a single vertical drain pipe, but there are some limitations. The minimum size for the standpipe and trap is 2" in the US and Canada(is the new piping 1 1/2 or 2"?). Pic 6 doesn't look like there's a trap in the new piping. The unused wall stubout should have been capped to prevent sewer gas from entering structure. You shouldn't have a problem with HE machine.
Edited 1 times.
|
|
Post Reply
|
|
Author:
steve (CA)
Picture 1 could be turned into picture 4, if the new standpipe and trap are 2", and if the vertical in-wall pipe is receiving waste from above storeys, there's a limit of 4 fixture units per storey that can drain into that vertical pipe. If more than 4 fixture units per floor drains into the vertical pipe, the vertical pipe can't be a wet vent for the new washer drain and a separate vent would be required. Picture 2 is completely illegal. The new trap and standpipe in picture 4 appear to be 2", based on the diameter of the yellow plunger handle, which is usually about 7/8". Picture 3 would be legal, if the new standpipe, trap, trap arm and through-floor pipe is a minimum 2". New vent can be 1 1/2".

|
|
Post Reply
|
|
Author:
ArthurPeabody (NM)
UPC 804.1 'Standpipe Receptors' reads, 'No standpipe receptor for a clothes washer shall extend more than 30 inches (762 mm), or not less than 18 inches (457 mm) above its trap. No trap for a clothes washer standpipe receptor shall be installed below the floor, but shall be roughed in not less than 6 inches (152 mm) and not more than 18 inches (457 mm) above the floor.' I don't know the rules in Canada, but that's good advice anywhere.
|
|
Post Reply
|
|
Author:
steve (CA)
The only things I'm seeing in the Canadian code is a 24" minimum length of the standpipe and the top of the standpipe shall be above the flood level of the washing machine.
|
|
Post Reply
|
|
Author:
Fuzzypink (Canada)
Thank you for your time and for helping me find the answers.
Kim
Edited 1 times.
|
|
Post Reply
|
|
Author:
Fuzzypink (Canada)
Thank you for your time and your detailed answers.
Kim
Edited 1 times.
|
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:

|