Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
conner172 (MN)
I'm replacing my old galvanized drain pipe with DWV PVC. The galvanized pipe connected vertically to the bathtub drain and then into a sharp 90 degree elbow to pickup the horizontal drain pipe. About 3 feet further along was a p-trap. About 4 inches after the p-trap was a sanitary tee with one end plugged and the other end running into a horizontal pipe which traveled back the way the drain had come from about 3 feet where it ended in a sanitary tee with the other horizontal end plugged and the vertical end picking up the vertical vent. It seems to me this was not code compliant, because the vent goes horizontal below the level of the bathtub drain fitting.
In my planned configuration, I want to put the p-trap right under the bathtub drain/overflow tube outlet, and then pickup the vertical vent 4 inches after the p-trap. The problem is that the vertical vent is located 5 inches horizontally away from the p-trap. In order to pickup the vertical vent, I'd need to place a 45 after the p-trap to begin the bend, another 44 going the other way to straighten the bend, pick up the vertical vent with a sanitary tee or wye, and the repeat the 45 degree bends going in the other direction to realign with the original direction of the drain run. I'm trying to avoid any horizontal vent pipe below the bathtub drain fitting.
|
Post Reply
|
Author:
steve (CA)
Can you post a picture of the existing configuration and a sketch of what you plan to do?
|
Post Reply
|
Author:
conner172 (MN)
It looks like I can only upload one at a time. Here's the existing layout.
Existing
[drive.google.com]
|
Post Reply
|
Author:
steve (CA)
Roll the vent tee/wye 45* and then 45* fitting to go vertical. 45* is considered vertical. The only "wet vent" you have is the vertical section of 4" between the toilet and sink.

|
Post Reply
|
Author:
conner172 (MN)
Thank you! I wasn't aware that a 45* is considered vertical. I thought I had to use the fitting either horizontally or vertically, but could not use it at a 45* angle.
Thanks again!
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:

|