Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
Tom130 (IL)
You need to replace that expansion tank. While it's off make sure the gauge reads zero. If not replace the gauge. If it goes high again after filling the system you may need to repair or replace the pressure reducing valve (last 3 pictures).
|
Post Reply
|
Author:
Lee (NJ)
One more question.
Boiler Pressure per gauge is at 30 Psi, after I installed the new expansion Tank. Obviously the boiler pressure is too high. I believe pressure should be at 12 Psi to 15 Psi . The boiler, if I remember correctly, always ran at 20 Psi. I apparently made a mistake during the installation process. Presently, I tapped on the new expansion tank and the new expansion tank seems to be half full/ half empty. Because of the tapping on the expansion tank I believe the tank is still good and not ruined. I thought I ruined the expansion tank when I added air to the expansion tank with my compressor. Tank is definitely still good. I thought I needed to add air to the expansion tank because my tire pressure gauge did not register or move when I checked the air pressure(with two tire pressure gauges).
Question : do I let air out of expansion tank at the valve ? Or do I put more air in the expansion tank ?
Do I first need to isolate the top floor of the radiators or close off/ isolate the water to the cast iron radiator on the top floor(single floor Ranch house) then once I have closed off or isolated the top floor - turn the boiler drain valve and drain the boiler and subsequently the water will drain out of the expansion tank while watching my boiler pressure gauge and then address the expansion tank either add more air or take air out at the valve of the expansion tank ?
Appreciate some help big time !
|
Post Reply
|
Author:
Tom130 (IL)
The pressure reducing valve sets the pressure in your system. Assuming you haven't changed the adjustment screw it's probably letting too much water into your boiler. You can try adjusting it but you'll probably end up rebuilding or replacing it. As long as the relief valve isn't dripping too much pressure isn't a big problem.
|
Post Reply
|
Author:
Lee (NJ)
Hi Tom130 !
Thank you for all your help. I am guessing the original Plumber who installed the Boiler must have set the Pressure Reducing Valve to 20 Psi. I noticed when I opened the boiler drain valve(red handle) at the bottom of the boiler, the pressure kept or stayed at 20 Psi. The Pressure Relief Valve I just installed. So the Pressure Relief Valve is new. The Pressure Relief Valve is not dripping. I should be Ok it seems.
During the original installation of a boiler ; does the Plumber measure the water pressure coming from our Town and then adjust the water Pressure Reducing Valve to match the pressure the boiler manufacturer requires ? I looked at the Pressure Reducing Valve it says on the label that it is set at 12 Psi from Bell and Gossett. Apparently either the Pressure Reducing Valve is set at 20 Psi by the Plumber at the time of original installation of the boiler or the Pressure Reducing Valve is broken ?
I still kind of think I screwed up the installation of the expansion tank. I am really glad the Pressure Relief Valve is not dripping. I did kind of think that is what matters in the long run. Sorry if I am being a Pain in the Rear End over here in NJ(approximately 45 minutes from the City) ! I have always been interested in Plumbing and Electrical, actually, and having "understanding" is really interesting !
If I remember the boiler always had a pressure of approximately 20 Psi now the pressure is just under 30 Psi. That is why I believe I screwed up the install of the expansion tank. I do realize that for a "Homeowner" the standards are less. I certainly am not a Professional or a trained Tradesman. I am able to keep the "lights on" by doing a thing or two whenever I can. Well, Tom thanks for all your help. Again sorry for going on and on. I do find Plumbing interesting. Plumbing is, in my opinion, the most important Trade their is. Without Water Humans could not live. Thank You. You the Man !
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|