Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
Snickers (MA)
Our Burnham oil boiler v13A (42 years old) is running almost constantly when turned on. A rattling noise from the circulator. It provides heat and hot water. Keeps firing as if not controlled by thermostats or controller. Two Taco zone valves 571-2. Two zones have two new Honeywell nonprogrammable thermostats. One zone appears better than the second in that it doesn’t exceed more than 10 degrees above set point. Zone 2 is worse. If the set point is 65, it keeps hearing to 78-80 degrees F or until I turn it off. The aqua stat is Hunnewell 1297L. Both levers on the zone valves are fixed at open. Aqua stat at 180 high and 150 low. Taco circulator pumps. Carlin burner motor. Transformer volts work.
When push reset on aqua stat, and it is not running, it won’t turn on. When it is running and press, it won’t reset. Honeywell aqua stat is 1297L. So far, had programmable and replaced with new nonprogrammable, thinking this is reason burner is not controlled by thermostat. The burner on and off works from the emergency switch and boiler. There is 24v at burner for thermostat wires. When remove the wires from the burner, it continues to run. When turn off thermostats, it runs. We vacuumed some of the burner and vents. Pipes hot above valves. Thanks in advance for any suggestions. I can provide photos. When off it continues to make noise in pipes.
|
Post Reply
|
Author:
Tom130 (IL)
When you say "Both levers on the zone valves are fixed at open" do you mean the valves are in bypass instead of auto mode? Why? Have you tried it in auto?
|
Post Reply
|
Author:
Snickers (MA)
Tom- yes. The zone valves are in open manual instead of Auto. The last technician moved it to open and I don’t know reason. I just placed both levers to Auto to see if this works.
Update: Thank you. The boiler is working better now that I set zone valves to Auto. It seems this was the problem. It is still firing when the thermostats are off, but it stayed off for at least an hour after I turned it to Auto. I will give it time to see if it works. Thank you.
Edited 3 times.
|
Post Reply
|
Author:
Tom130 (IL)
That's what I'd expect. The aquastat keeps the boiler at temperature and the thermostat opens the zone valve which tells the circulator pump to run.
Edited 1 times.
|
Post Reply
|
Author:
Snickers (MA)
Tom, Thank you!
The problem is solved. The zone valves on auto are working, and heat is shutting off at set temperatures. This was a great learning experience.
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|