Over 700,000 strictly plumbing related posts
Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
sum (FL)
This is inside the kitchen sink cabinet. I am replacing the drain piping, the hot and cold supply valves, and at the same time, mounting a new 3/16" piece of thin plywood to cover the existing cardboard.
The problem is, the supply piping is CPVC, and connected to a compression valve. I have 9 others to do similar to this.
Once the compression valve was off, I couldn't get the brass ferrule off.
Tried using a plier to rotate off the pipe, didn't work.
Next I have a sleeve puller, but that was designed for copper, so the piece of adapter that goes inside copper tubing didn't fit the smaller ID CPVC, so the sleeve puller didn't work.
Normally I would just use the existing ferrule and nut onto a new valve, but in this case, I want to install a new piece of board on the back side of the sink cabinet, than put in new escutcheons and new valves.
Besides, the ferrule has been chewed on by my plier so much it's deformed. It needs to come out. I am not even sure the CPVC pipe is any good as I might have manipulated it too much as well.
Any suggestions?
My next step will be to use a Dremel to cut across the ferrule and try to split it with a flat head screwdriver.
Is it a bad idea to use a compression stop on CPVC? Is there a better option? Sharkbites?
|
Post Reply
|
Author:
DaveMill (CA)
Dremel is your best friend here. Go super slow, watch closely to make sure the brass chips don't suddenly become CPVC chips. Good quality cut-off wheels are far superior to the brittle super-thin junk, especially when you are working under a cramped sink.
|
Post Reply
|
Author:
packy (MA)
sum... i would just cut the flange off the wall. make the hole you're drilling big enough to slide over the nut and use a split flange to cover the hole.
|
Post Reply
|
Author:
sum (FL)
Packy, the problem is at this point due to my numerous attempt to try to get it off, the brass ferrule has bite marks on it from the plier as I tried to rotate it off the pipe; in the process of doing so the ferrule also bite onto the CPVC as well I can feel with my finger. I don't think the ferrule is round anymore.
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
sum, i don't have much experience with cpvc. up here north of boston we don't see it at all.
but, since you are covering the wall with plywood, why don't you open up a bigger hole and repipe from a good area of the piping ?
|
Post Reply
|
Author:
Tom130 (IL)
Or cut it right behind the ferrule and use a glue on cpvc stop.
|
Post Reply
|
Author:
sum (FL)
The problem with a glued on stop is in the future if it needs to be replaced you have to cut it shorter again until you are left with no pipe.
|
Post Reply
|
Author:
sum (FL)
Packy, I agree with you.
The only thing is the time constraint. Right now the old countertop and sink have been removed, faucet removed, disposer removed, and so I have some room to do stuff that's impossible once the sink cabinet becomes crowded again.
The countertop guys are coming on Friday, so I am trying to figure out what I can do between now and Friday during the evening hours that I can spare to attack this head on.
I used a Dremel to cut the ferrule off for both the hot and cold side. I did accidentally scored the plastic a little on the cold side. As you can see, as soon as the ferrule was cut through, it popped open with a gap of about 3/16". Even with it cut open it was very difficult to get it off the pipe due to the degree it was strangled. It actually left a narrow neck and I don't think a sleeve puller would have worked anyway.
after thinking about your comment, I went ahead and cut away the back of the cabinet, it was a cardboard anyway. It exposed the CPVC pipes and PVC drains with some of the crumpling sheetrock I pulled off.
I may open a bigger hole tomorrow, but whatever I do need to be wrapped up by Thursday.
|
Post Reply
|
Author:
steve (CA)
Sum, how about cutting the cpvc at the outer edge of the ferrule? The ferrule might slide off. The section of the pipe that the ferrule is on would be buried in the stop and the new ferrule would be on unmolested pipe. The stub is long enough to lose that small amount.
|
Post Reply
|
Author:
sum (FL)
So the question I have is what is the best way to terminate these CPVC pipes if I want some flexibility in replacing the valves in the future?
I don't think compression connections is a good idea. With the sink installed, and a disposer, and faucet with everything hooked up I do not think I can remove a compression valve with a crimped tight ferrule like I was able to do tonight.
A cement on CPVC stop means I will have to cut it shorter next time.
What do you think of a CPVC male adapter, than onto it a 1/2" female threaded stop valve, this will allow the valve to be removed in the future and replaced if necessary. The down side is when the stop is tightened you night end up with the branch at 9'O'clock when your hose is coming in at 3'O'clock.
Another option is to use Sharkbites, which I have always avoided but in this case it's easy and serviceable.
I supposed one way is to tighten a compression valve such that it doesn't strangle the plastic, but I don't I have the skill/experience to do that without it leaking.
I am changing out valves in two other bathrooms in this unit, so 7 more valves to deal with and I want to take the same approach to all.
|
Post Reply
|
Author:
steve (CA)
Sum, screw the adapter into the valve before gluing the adapter to the pipe. You can get your orientation this way.
|
Post Reply
|
Author:
sum (FL)
steve, you are right I could just assemble the valves first then cement them on. That should work unless the threaded connection leaks and I have to tighten it another quarter turn LOL.
|
Post Reply
|
Author:
sum (FL)
anyone know how these fittings are made?
How does the metal and the plastic mate inside? Will the different thermal expansion of the metal vs plastic cause potential leaks especially on the hot side?
|
Post Reply
|
Author:
steve (CA)
There's an o-ring inside to seal the dissimiliar materials. I've seen some that have both an o-ring groove and a separate groove for the CPVC to mould into and retain the 2 parts. The one in the link has combination o-ring and retainer in one groove.
[www.pvcfittingsonline.com]
----
This fitting is available at
[www.plumbingsupply.com]
Edited 1 times.
|
Post Reply
|
Author:
sum (FL)
steve, thanks for the link that makes sense.
I came across some that looks like this...seems like these are a bad design to avoid, to connect and disconnect one has to put a curved jaw plier on the plastic side to hold it steady to allow a wrench to tighten or loosen the connecting valve. It seems this may stress the plastic and the o-ring. I like those where the exposed metal half has a hex or flats so you can hold the metal side with an adjustable wrench.
|
Post Reply
|
Author:
steve (CA)
Those fittings might have a hex(?) shape on the brass to keep them from spinning in the plastic. I would prefer the stainless that you posted.
|
Post Reply
|
Author:
packy (MA)
so... use a thinner body metal brass slip nut.
BTW, those plastic hangers are affectionetly known as mickey mouse ears and yes they hold well enough. remember you must allow for expansion.
|
Post Reply
|
Author:
sum (FL)
Packy, the right side drain will not be used. I will use the center drain for both sink (one regular one with disposer). You gave me the idea of using a female adapter to thread onto that male threaded end, and I think I will just cement a short piece of pipe to it and a cleanout adapter with a CO plug and leave it at that. Unless there is a more direct way to close it without using two back to back female fittings.
The old mickey mouse clamps were cracked at the screw holes, I don't know if they were cracked on the day it was installed broken by driving the screw in with an impact driver, or it was cracked later on. Do they make metal versions of these suspension clamps?
|
Post Reply
|
Author:
packy (MA)
sum, i'd be very careful with metal hangers wrapped around plastic pipe. . think abrasion..
you can take a 3/4 or a 1" copper clip and bend the ends inward and give them a twist with some pliers. wrap some rubber (like inertube rubber) around the pipe and fasten that.
|
Post Reply
|
Author:
steve (CA)
Sum, you could use perforated plastic strapping. From the face of the wood strip, over the top, around the back of the pipe and back down the face of the wood strip. This will keep the pipe from pushing back in the wall.
|
Post Reply
|
Author:
sum (FL)
steve, I used new suspension clamps around the CPVC pipes, but Packy's warning about not making them too tight to allow for expansion especially the hot side so I didn't squeeze the clamps all the way. Still have movement if I push in or pull out hard like when putting on a temp Sharkbite cap or valve.
So I am going to try your plastic strap on top of the clamps since I have some left over. I have copper straps too if you think that may be better.
|
Post Reply
|
Author:
sum (FL)
The countertop company was supposed to be here on Friday but called to postpone due to their previous project took longer than anticipated. So now I have the weekend to finish all my stuff in the sink cabinet which is better because I'd rather work in there without the sink easier on my back.
I kept going back and forth on how to terminate those CPVC supply lines, from the way they are strangled I question how reliable another compression connection would be, I have been using sharkbite valves and caps as a temporary measure and that held with no leak so that's an option just sharkbite valves, or go with a CPVCxMIP where the MIP side is metal and I can thread on FIP valves. This is not just the two kitchen valves but also two other bathrooms (one of them has two sinks) so all together I have ten CPVC connections to deal with and I suspect they all have this issue with the compression ferrule strangulation.
I am beginning to warm up to the idea of transitioning to copper piping at the wall. Basically leave say 1.5" of CPVC pipe and cut away the strangled section, then solvent weld onto it a Sioux Chief 643-211 CPVC X MALE SWEAT FITTING ADAPTER:
[www.siouxchief.com]
This gives me 11" of copper tubing to cut back to say 2" or so and I can connect to regular compression valves that I never had an issue removing the ferrule with a sleeve puller.
Do you think this is a good solution?
I know the best solution is to cut the CPVC behind the wall at a vertical position, then transition to an L shaped copper stubout, but the pipes didn't terminate at these locations and the cold side runs up to somewhere else...and I had to close up the wall fast to get ready for their Friday install so I am left with options to modify the stubouts.
|
Post Reply
|
Author:
vic (CA)
Sum, it seems like you've really thought this out, have enough experience and so that sounds like a good plan to me.
|
Post Reply
|
Author:
sharp1 (IL)
Can plastic ferrules be used for CPVC with compression stops? I know that the brass reinforcements will also slide snugly into the end of the CPVC pipe.
|
Post Reply
|
Author:
Don411 (IN)
This is probably the best option, it gets you out of the plastic onto more durable copper for future servicing.
|
Post Reply
|
Author:
sum (FL)
I am not sure. I have only used plastic ferrules with plastic nuts in smaller sizes like in 1/4" icemaker lines. Don't know about 3/8" or 1/2" connections.
|
Post Reply
|
Author:
george 7941 (Canada)
Plastic ferrules only work on pipes soft enough to compress under the low forces exerted by plastic ferrules. Will work on PB lines but CPVC is too hard for the plastic ferrule to bite into and the compression fitting could slide right off under pressure.
Before the advent of the braided supply lines, polybutylene lines were common and I installed a lot of them using plastic ferrules.
|
Post Reply
|
Author:
Curly (CA)
I use Pasco Angle On Wrench #4525. It will work for 3/8" compression and 1/2" male iron pipe.
I use it all the time.
|
Post Reply
|
Author:
sum (FL)
Curly, OMG I didn't know such a thing existed. This will make a huge difference in allowing me to hold the valve steady to tighten the other nut! Thank you thank you thank you!!! This forum is great another solution to a problem that's been troubling me for a while. I even removed the handles of these valves just to get a better bite!
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|