Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
Temu Chechu (MN)
Hi,
Thanks in advance for your answer. I'm confused about wet venting. My understanding is that it is allowed for a bathroom group. Each drainpipe must be increased by one pipe size and there is one vent (lav) that vents all the fixtures (shower/tub, lav, toilet)
Normally a lav needs 1/1/4 drain so that is increased to 1.5 inch drain.
Normally a toilet needs a 3 inch drain so that is increase to 4 inch.
Normally a shower along (not a tub) needs a 2 inch drain. So I guess it would need to be increased to 2.5 inches which doesn't really exist so it would need to be increased to 3 inches?
Is this true and if so when does it need to go from 2 inches to 3 inches? The shower drain is 2 inches. Does it need to increase right away on the tailpiece?
Also, if I recall the pipes need to connect in a specific order?
|
Post Reply
|
Author:
packy (MA)
only the piping that is acting as a vent/drain combo needs to be increased in size.
the shower vent would normally be 1 1/2 inch so it gets increased to 2 inch.
that 2 inch then accepts the lav drain which is 1 1/2 inch.
the toilet does not act as a vent in any way so it stays 3 inch.
|
Post Reply
|
Author:
steve (CA)
Some codes require the toilet to be the most downstream fixture. The drains for the wet vented fixtures enter the horizontal drain pipe from a horizontal direction and the vent connection enters the horizontal drain pipe from a vertical direction. Some codes require the toilet to have a 2" minimum vent size, so if you are using the sink drain as the vent for the wet vented fixtures, the dry vent above the sink drain would also need to be 2". Check what your local codes requires. Often times the local building department has paper/online "handouts" with common code items for kitchen or bath remodels.
|
Post Reply
|
Author:
brucezh (MI)
You're right that wet venting is allowed for a bathroom group, and each drainpipe typically needs to be increased by one size. For example, the lav’s 1 1/4-inch drain would be increased to 1.5 inches, and the toilet's 3-inch drain stays at 3 inches unless local codes require 4 inches. For the shower, since 2.5 inches doesn’t exist, it would be increased to 3 inches. As for when the shower drain needs to increase, it usually happens before the drain connects to the main stack, but it’s always good to double-check with local codes.
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|