Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
Jdawest1 (TX)
This is my first post so I’ll try to get all the info in here I can.
I have a 40 gallon electric water heater, it’s a Rheem. It’s been running continuously and I figured it out because of my 900 dollar water bill. So I pulled off the top thermostat and replaced it. It’s the long thermostat like 3 inches. My bottom part that the wires go to doesn’t have a temp fail so I assume that’s not a thermostat.
Anyway, after putting on the new one I tested voltage and have 120 and 120 ok top element and same on bottom.
Let it run for about 7 hours and remembered that I should check it to make sure it’s off.
Tested it and still has same voltage. Sooo I turned it down from 125f to 90f thinking that would turn it off, nope same voltage reading. The pressure relief valve on top is not connected to the pvc pipe and that’s gonna be my fault from when I changed out the heater in 2014.
So I’m lost, did I get a bad thermostat? Also I blocked in the water valve to it for about 30 minutes with the temp reduced to 90 and same thing, 240 on each element. The outgoing side on the copper pipe is a little warm, maybe like 80-90 I mean not hot al all so I don’t think it’s passing water through it or if that is even possible lol.
Any suggestions would be appreciated. I know you folks are busy so thanks in advance.
Don
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
plumber/electrician YESTERDAY
|
Post Reply
|
Author:
packy (MA)
a very high water bill means there is a leak somewhere. replacing the t-stat doesn't help. it is doing it's job trying to keep the water hot.
find and fix the leak and all should be well..
|
Post Reply
|
Author:
Jdawest1 (TX)
Thanks Packy. I’ll look into how to check and see if it is leaking by. I know I had not used the hot water for about 7 hours before I tested it and I did notice the out going pipe from the water heater was warm so maybe it’s leaking by I guess.
|
Post Reply
|
Author:
bernabeu (SC)
it is NOT 'leaking by'
somewhere in your hot water piping there is a leak
turn every fixture including the ice maker off and look at the 'leak detector indicator dial' on the water meter
DO NOT VALVE OFF THE HEATER, we are LOOKING for a leak, not trying to stop it at this point
it will be a 'small' pyramid, star, triangle which spins when ANY water is used
if this dial is turning AT ALL with no water being used at ANY fixture then you HAVE A LEAK
ASCERTAINING that a leak exists is EASY.
?FINDING IT NOT SO MUCH!!
|
Post Reply
|
Author:
Jdawest1 (TX)
Ahhh ok. Perfect I’ll try that and post back what I find out.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|