Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
Noko77 (AZ)
Can someone please help me with this? I have a dedicated recirculation hot water system in my house. I know it is dedicated, because I have checked under the sinks for crossover valves, and there are none. The system works perfectly, except for one problem.
About a month ago, I suddenly started getting warm to very warm water (way past lukewarm) at all of the cold-water faucets. This was the FIRST time this ever happened in twelve years, so I knew something had changed.
I checked the pressure, which was very high (130 pounds), so obviously the PRV was bad, and I had it replaced. I thought that might be causing the trouble. Now the pressure is 55 pounds. But I still get warm water from the cold faucets!
If I turn the pump off, and wait a few hours, everything is near normal (much colder from cold faucet).
My floors are not hot, so I don't think there is any under-slab leak. Since turning the pump off seems to cure it, I am baffled.
The only other component I can see in the system is a check valve between the pump and the water heater. I can't see how this would affect anything.
[i.postimg.cc]
So what changed?
Thank you.
Edited 6 times.
|
Post Reply
|
Author:
bernabeu (SC)
The check is bad.
When you valve off the pump the issue disappears.
The check 'should' act as a shut off valve when the pump does not run else there is a cross connection with no 'flow'.
Edited 1 times.
|
Post Reply
|
Author:
Noko77 (AZ)
Quote: Author: bernabeu (SC)
The check is bad.
When you valve off the pump the issue disappears.
Thank you. I should have mentioned that I did not operate the valve to the pump (but I will try that). I just unplugged the pump.
As far as I can tell, I do not have the red line shown in your diagram marked "A" that is attached to the cold water supply at the top. The line just goes from the pump straight into the bottom of the heater.
Do you mean the check is stuck open or stuck closed?
Thank you again.
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
stuck open
Edited 1 times.
|
Post Reply
|
Author:
Noko77 (AZ)
I am having a really hard time understanding this system.
My system looks exactly like this (comments in red are mine):
[i.postimg.cc]
I can't understand how hot water can *ever* get on the cold side. Even if the check valve is stuck open.
Thank you.
I really appreciate your help.
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
'google' {gravity circulation}
the pump itself will RESTRICT, but not stop, it
the check stops it cold (pun intended)
(gravity circulation will occur with the 'b' connection since the water at the top of the tank is warmer than the bottom and induces a 'draft effect')
|
Post Reply
|
Author:
Noko77 (AZ)
I'm pretty dumb about this stuff, but it drives me nuts if I can't figure it out after looking at it for two days. I couldn't sleep last night because of this, so I was up at 4AM checking and rechecking the leak indicator on the water meter.
Yes, I can see how the gravity circulation would happen if the check valve was open and the pump was off, but it seems it would just be circulating water from the tank back into the *hot* loop.
But how does *any* hot water *ever* get onto the *cold* side in a dedicated system? I can't see the connection between the hot water side and the cold side. I keep thinking I have some kind of a mental block on this.
It's not just a little bit warm. The cold supply is about 77 degrees, I have measured as much as 99 degrees coming out of the cold faucet.
Thanks.
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
valve off the circ pump
if problem goes away you have confirmed a bad check
if problem persists you may have a crossover at a shower or possibly the washing machine or another single lever fixture
perhaps time for an actual onsite plumber
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|