Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
major sisu (MN)
I installed a new vanity and discovered I need one more inch of clearance for the P trap to fit.
I can put two 45 elbows to the drain pipe to make the P trap fit.
Does this meet code in MN.
If not, can I cut a hole in vanity shelf for the P trap to fit?
Any other suggestions besides opening the drywall.
Thanks
|
Post Reply
|
Author:
bernabeu (SC)
yes, the pic is an "S" trap
it is NOT code compliant
yes, by all means notch out the cabinet bottom as required
BUT
a small leak may thereby be invisible and do (major) damage
OR
open the wall and 'do it right'
|
Post Reply
|
Author:
major sisu (MN)
There is drawer under the shelf so all is good.
I don’t even think the p trap protruding through the shelf will hinder the drawer.
Thanks for the reply.
|
Post Reply
|
Author:
bernabeu (SC)
if I had bought the wrong cabinet I would simply remove the cabinet bottom above the drawer COMPLETELY and 'fix' the drawer itself in place
externally pleasing
internally fully functional as a standard cabinet
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
sum,
agree
but
that is a purchased 'stock' cabinet
said 'design' will not work for the OP as HIS drawer is in a separate lower 'compartment'
modification after the fact would be more $ than a new cabinet
|
Post Reply
|
Author:
ArthurPeabody (NM)
Would venting it before the angle down make it compliant?
|
Post Reply
|
Author:
bernabeu (SC)
yes, but an AAV is only permitted when it can NOT be properly vented
the expense of opening a wall or replacing a cabinet will NOT qualify as a reason for an AAV
|
Post Reply
|
Author:
Don411 (IN)
Quote bernabeu ...the expense of opening a wall or replacing a cabinet will NOT qualify as a reason for an AAV...
I'll bet that 99% of homeowners say that it DOES....
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: