Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 air vacuum relief valve replacement
Author: leakyring (AR)

I have a Marathon water heater in a rental that just malfunctioned and flooded the house. It looked loke lime hadbuilt up and opened the valve releasing water. Can I use a plug to go back or is it aboslutely necessary to just get another valve. Water heater has a pressure relief valve which is piped to outside, but this air vacuum valve releases into the buildings' closet and everywhere else then. I was told only a plastic tank unit has to have this valve installed. But is a poor design flaw if when it opens and floods everything. Any advise, expertise is apprecciated

Post Reply

 Re: air vacuum relief valve replacement
Author: bernabeu (SC)

a plastic tank MUST have a vacuum relief valve

either

replace said valve

or

replace the tank with one not requiring said valve



ps. quality plumbing is expensive, crap plumbing is MORE expensive

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: air vacuum relief valve replacement
Author: packy (MA)

this is from the phoenix code..504.1 Antisiphon Devices
An approved means, such as a cold water "dip" tube with a hole at the top or a vacuum relief valve installed in the cold water supply line above the top of the heater or tank, shall be provided to prevent siphoning of any storage water heater or tank.

Post Reply

 Re: air vacuum relief valve replacement
Author: bernabeu (SC)

packy,

'most' marathon as well as 'some' rheem are 'lifetime' plastic and require 'anti collapse' external vacuum breakers to prevent a MECHANICAL failure of the tank


different protection than anti siphon



as a WAG an atmospheric vacuum relief may have been installed instead of a MORE EXPENSIVE pressure vacuum breaker

atmospheric breakers fail totally when the 'duckbill' blows out, pressure breakers merely start to leak

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 1 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.