Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
timothy108 (CA)
I am wondering if anyone knows of a commercial kitchen sprayer unit that has built in check valves?
|
Post Reply
|
Author:
bernabeu (SC)
[www.plumbingsupply.com]
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
hj (AZ)
All commercial sink pre-rinse units, Chicago, T&S, etc. will have check valves.
|
Post Reply
|
Author:
timothy108 (CA)
Awesome...thank you for the information
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
.... since the hose will allow the water outlet to be lower than the flood level rim of the fixture a backflow prevention device is REQUIRED BY CODE else the fixture will NOT be 'approved' ....
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
Most prerinse devices have a shorter hose with a spring mount to keep it above the water level.
|
Post Reply
|
Author:
bernabeu (SC)
That is true WHILE THE SPRAYER IN "ON THE HOOK", but, it is often used OFF the hook allowing it to be pulled down in which case ............
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: