Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Condensate won't flow to drain
Author: pLongos313 (MA)

I had a new draw through, upflow air handler installed with new duct work. Problem is the condensate won't flow to the drain, but stays trapped behind the evaporator coil. I believe this is due to the suction of the fan. The contractor increased the previous plenum size along with changing a few ducts from 6" to 7" even though he NEVER did any calculations. The previous set up worked perfectly and now all i can hear is water gurgling as the volume keeps increasing. He tells me nothing is wrong, but this unit is not operating efficiently or as intended. If I move the filter a little water starts to flow. It is pitched right. The p trap works as intended if i take off the filter. Its an open return so I am not sure how to decrease the static pressure behind the evaporator coil (0.5 wc). If the plenum was smaller won't that increase the air velocity? I attached the p trap pics. I am thinking the plenum is too big which is requiring more air volume which means the blower needs to work more, thus increasing the static pressure. Any insight will be much appreciated.

Post Reply

 Re: Condensate won't flow to drain
Author: bernabeu (SC)

The trap needs to be a 'deep seal' type and LOWERED in relationship with the elevation of the pan.

The inlet pipe to the trap needs to be vertically long enough (H) for a 'head' of water to accumulate to 'force' flow.

The trap needs to be deep enough (H/2 minimum) so that the seal is not 'sucked away'.

One must ALSO allow for an increase in suction as the filter ages.

In your case I would allow 1-1/2 for H, and 2 for H/2+.




H = pressure of air handler instilled by the fan - ask your installer for a 'magnehelic' reading




Typical 'proper' installation:

[f01.justanswer.com]


The following is 'how not to':





Edited 3 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.