Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Refill Boiler System
Author: mekjean (NJ)

I shut the water the off to my hot water system and I drained my boiler through the drain valve to replace circulating pump and pressure relief valve that were very old. No problems. I have an old American Standard Boiler. I went to turn the water back on, but system did not refill. I know the valve is good, recently upgraded. I am stumped why it won't refill. Since system is old should I try to refill back through the boiler drain vale? Any help would be appreciated. Thank you.

Post Reply

 Re: Refill Boiler System
Author: bernabeu (SC)

If you KNOW that the valve is actually open then the only other explanation is that you have no air vent open at the top of the system

OR

an 'auto-fill' PRV valve is inoperative.

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Refill Boiler System
Author: bsipps (PA)

I would tend to think the auto fill also hopefully you changed the temp/ pressure gauge while the system was empty also

Post Reply

 Re: Refill Boiler System
Author: packy (MA)

as my friend from SC surmised.

mosy likely the auto fill valve is stuck closed. it is a common problem.

it will need to be replaced.

as a tempory fix you can back fill it through the boiler drain valve. a washing machine hose will do the trick.

watch the pressure gauge. don't let the system get above 30 PSI or the relief valve will blow.

once full, set the pressure to 12-15 PSI.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.