Plumbing advice, answers, information, help and suggestions are provided here by experienced plumbers who wish to "give back" to others. Since 1996 we have been the best online (strictly) PLUMBING forum. If you have questions and are looking for answers or wish to discuss anything about toilets, sinks, faucets, drainage, water filters, venting, water heating, showers, pumps, and other exclusively PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
eggman2112 (Canada)
Our building in Richmond Hill, Ontario, Canada has a regulator / backflow preventer that is permanently set to 175 PSI.
Our water heaters all have T&P valves that are 150 PSI and are residential Space Saver type. This was built by very large construction company (Urbacon).
Why would they use residential water heaters instead of commercial ones?
Why would they have T&P valves that are below the building water pressure?
The T&P on 4 water heaters are always leaking (with no drains provided) until we replaced one T&P with a 175 PSI and now no more leaks.
If you had an expansion tank wouldn't it just fill up until it could fill anymore then the T&P would start leaking again?
We had a few plumbers that still can't figure out why the hot water tanks keep leaking without changing the whole building water regulator / backflow preventer to a lower one if they even make one.
Just trying to make some logic of why they would build that way. Thanks for your info.
|
Post Reply
|
Author:
eggman2112 (Canada)
Here is a pic of the water pressure that we measured which seems to sit about 80 PSI but can get up to 180 or 190 PSI.
[mega.nz]
|
Post Reply
|
Author:
bernabeu (SC)
Y'all need a better dual or perhaps triple stage regulator to prevent 'creep' under no or low flow conditions.
Y'all 'should' have a pressure compression (expansion) tank sized for the entire building.
Y'all need better plumbers on site.
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: