Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 weird issue with simple drain frowning please help
Author: imcool (MI)

The Sink drain broke so I replaced it.

Before sink drain replacement, everything was functioning properly until I disassembled abs piping out and the Rubber join coupler (abs 1 1/2 to copper 1 1/4). After reassembling it, the P trap is not draining correctly, and it only drains when the nut of the Rubber join coupler is kept loose ( Check photo ) .

However, if it is kept loose, it leaks drain water. Previously, the same Rubber coupler/joiner was working fine before I opened it.


Could you kindly suggest a solution for fixing this issue with the current setup?

Alternatively, would it be possible for you to recommend a better replacement or installation method that would prevent this issue from recurring in the future?

Unfortunately, I cannot remove the copper drain pipe as it goes into the basement, and it would be quite inconvenient to replace it at this time. Thank you for your kind assistance.

Removed Tee in last doesnt have any vent.









Edited 3 times.

Post Reply

 Re: weird issue with simple drain
Author: bernabeu (SC)

You have an unvented 's' trap assembly and (probably) a 'partial' stoppage.

You will need an AAV added after the trap

BUT

first try to clear the stoppage.

NO CHEMICALS

Try a plunger - fill the sink and get the water ROCKING with occasional FORCEFUL downward pushes.

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638



Edited 1 times.

Post Reply

 Re: weird issue with simple drain
Author: imcool (MI)

I will install ABS vent,
As all the sink drains and pipes are out and disassembled, there is no clog anywhere.

I am confused by when you said its an S trap I have, but it looks like P trap. Can you clear this confusion?



thanks

Post Reply

 Re: weird issue with simple drain
Author: hj (AZ)

You DO HAVE an "S" trap, and you also have a stoppage, or partial stoppage, which traps air in the inverted "U" section of the trap. Loosening the coupling allows the air to escape and allows the water to drain. The drain line is full of water, but will drain when water enters the pipe.

Post Reply

 Re: weird issue with simple drain
Author: bernabeu (SC)

an unvented 'p' trap IS an 's' trap

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: weird issue with simple drain
Author: hj (AZ)

Which is why I said, "You DO have an 'S' trap.

Post Reply

 Re: weird issue with simple drain
Author: george 7941 (Canada)

I am having difficulty understanding why air in the trap, which affects pressures by at most 5in WC, prevents draining. When there is standing water in the sink, there is more than 5in WC of pressure forcing water into the drain pipe, so the water should still drain albeit more slowly because of the loss of 5in WC of pressure.

Post Reply

 Re: weird issue with simple drain
Author: packy (MA)

george.. i'm having trouble too.
if what our friend from SC says is happening then there are many thousands of the same type situation that wouldn't drain.

just so we don't look like fools, cut in an AAV.

Post Reply

 Re: weird issue with simple drain
Author: steve (CA)

Maybe the trapped air is not "in the trap", but trapped in the downstream piping BY the trap.

Post Reply

 Re: weird issue with simple drain
Author: george 7941 (Canada)

Even if there is air in the drain pipe downstream of the trap, the pressure from the standing water in the tailpiece and sink should force the air past any clog. even if slowly.

Post Reply

 Re: weird issue with simple drain
Author: packy (MA)

[www.plbg.com]

Post Reply

 Re: weird issue with simple drain
Author: george 7941 (Canada)

Ah! Lemon Plumber! I miss his posts.
In the linked thread, hj states that hydraulic principles hinder flow through double traps. I still don't get it.

Post Reply

 Re: weird issue with simple drain
Author: bernabeu (SC)

to quote hj:


You DO HAVE an "S" trap, and you also have a stoppage, or partial stoppage, which traps air in the inverted "U" section of the trap. Loosening the coupling allows the air to escape and allows the water to drain. The drain line is full of water, but will drain when water enters the pipe.


me: loosening the coupling serves the same purpose as a piped vent except allows sewer gass(es) to potentially enter the habited space

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: weird issue with simple drain
Author: imcool (MI)

I will cut a new AAV into the kitchen sink drain to fix this issue.

- What is the best way to connect abs to copper drain? should I stick to that frenco or there is any better idea.


- I would like to know why there is no AAV vent below the washroom sink I have? the washroom sink works works great but its smaller size than 1 1/2 kitchen drain pipe.

Cheers

Post Reply

 Re: weird issue with simple drain
Author: steve (CA)

The shielded coupling(Fernco) is fine to use. The lack of a vent isn't preventing the drainage, there's a restriction in the drain pipe. The vent keeps the trap from siphoning, which would allow sewer gas to enter the structure.

Post Reply

 Re: weird issue with simple drain
Author: imcool (MI)

can someone please tell me, how do i connect copper pipe to abs without using Frenco?

I tried looking online for fitting for my copper pipe size and abs size but I didnt find any fitting for my copper pipe frowning

copper drain pipe size is 1-1/4 Trade Size, 1.660 nom OD
ABS size is 1 1/2 inch.

Please share link for fitting frowning

appreciate your help

Post Reply

 Re: weird issue with simple drain
Author: packy (MA)

you would have to solder some sort of threaded adapter onto the copper. then find a fitting to screw to it on one end and glue on the other. then you'd have to cut the plastic and glue a coupling in there.

Post Reply

 Re: weird issue with simple drain
Author: bsipps (PA)

1 1/2” sweat X male adapter

Then use 1 1/2” tubular piping, tubular tee air admittance valve then a tubular trap and continuous waste if needed

Or use a fernco, abs piping with a trap that has a union for easy removal of the trap

Post Reply

 Re: weird issue with simple drain
Author: imcool (MI)

is the copper pipe 1 1/2 or 1 1/4.
I am so confused,
the OD i measured with caliper and the OD of the copper pipe is 1.6 inches

chart says its 1 1/4 inches pipe

please help frowning

Post Reply

 Re: weird issue with simple drain
Author: steve (CA)

Copper "pipe" is different than copper "tubing"(DWV, or type M,L or K). 1 1/2" copper tubing is 1 5/8" OD(1.625" ). You have 1 1/2" DWV copper tubing.



Edited 1 times.

Post Reply

 Re: weird issue with simple drain
Author: packy (MA)

my friend from PA. tubular doesn't always fit inside a male adapter.

Post Reply

 Re: weird issue with simple drain
Author: bsipps (PA)

You're right packy, I should have said trap adapter or (desanco)



Edited 1 times.

Post Reply

 Re: weird issue with simple drain
Author: sum (FL)

They do sell this whole contraption in one bag.



If OP knows how to solder I would cut the copper and solder on a brass trap adapter and plastic tubular the rest of the way.



Edited 1 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.