Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Taco ZVC and Intellicon HW+ added to system
Author: DoctorEd (VT)

Seeking some advise for the near-term and future.
(We live in upper New England and only use window air conditioners as needed during the summer.)
Our main energy use is oil which heats the house with the help of a wood pellet stove.

I have reviewed a lot of online blogs and videos, but because I have not studied how my system is currently running in any depth, I'm not sure about these items puzzling me so far.

My current heating system has the following:
-A zone for each floor of the house including the basement, = 2 baseboard heating zones plus a Modine for the basement.
-An indirect DHW storage tank wired as a fouth zone, it does not have a separate circulator only a zone valve.
-All 4 of the zone end switches are wired in parallel, and feed the Honeywell L8151A Aquastat on the T-T/3 terminals
-Each zone has its own setback thermostat (except the basement which uses a regular thermostat) connected to its zone valve, the DHW being run by the L4080B Aquastat on the storage tank for the 4th zone valve.
-The boiler is an Ultimate PFO-4 with a Beckett AFG burner and an R7184B burner control.

My first system upgrade will be to install a Taco ZVC406 to cleanup the zone valve wiring and provide me with a better system status.

My first question is this:
Should I move control of the system circulator to the Taco ZVC406, or leave it on the L8151A Aquastat C1 C2 terminals?

==

Next, I want to install an Intellicon HW+ on the L8151A Aquastat to try to optimize burner cycles and save some on fuel oil.

My second question is how to set the Intellicon?
I currently have the Aquastat set ~182 for the Hi Limit, the Lo Limit is turned all the way down (~110), and the Diff is set to ~15.
What would be your recommendation for the HW+ settings?
Should I change any Aquastat settings or leave them as is after installing the HW+?

==

In the future I might upgrade the Aquastat to an L7224U, but that might be down the road a bit.

Post Reply

 Re: Taco ZVC and Intellicon HW+ added to system
Author: bernabeu (SC)

wrong forum

you need a heating forum

==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Taco ZVC and Intellicon HW+ added to system
Author: packy (MA)

you can power the ZVC from C1-C2 saving you some wiring work.
the ZVC may have a prority for HW. meaning all other zones will not run when you have a call from the 4080. some people like this way, i don't.
182 for a high limit seems a little cool for northern NE ?
you don't want the low limit set that low. 160 would be as low as would use.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.