Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
DaveMill (CA)
Our 10-year-old house is on hill in the woods in the Santa Cruz Mountains of Northern California. Our water comes from our own well; we have a pressure tank that gives us enough water for irrigation. However, with extended power outages, we have seen pressure drop quite low in the house.
The foundation and retaining walls are well designed and recently inspected. We are working to stabilize the hill above the house with trees and bushes. We have excellent recommendations for species to plant from the local agricultural extension. We are planning a drip irrigation system.
My questions are, what sort of backflow prevention do I need to install on the irrigation system, and where do I install it? I assume I will run a 1" main irrigation line up to a valve manifold above the highest drip outlets. That line will be 50-75 feet long.
Thanks!
|
Post Reply
|
Author:
packy (MA)
generally a sprinkler backflow device is place on a tee before the water meter to save on the sewer bill.
in your case there is no meter so you locate the device where it will do its job but be able to be serviced/replaced when the time comes.
since your sprinklers will be located up on a hill you will need a special 'below grade' device.
you might have a chat with your local inspector as to which device they want.
BTW... there is the possibility of running the feed for the sprinkler piping all the way to the highest point (at least 12 inches above any head) and locate a standard backflow there with ALL the heads being downhill of it.
[www.google.com]
|
Post Reply
|
Author:
bsipps (PA)
Dave
I suggest a spill resistant vacuum breaker backflow device just remember to winterize the entire line that will be exposed to freezing conditions in the colder months
You could also use an atmospheric vacuum breaker both are testable
If you looking for something a little more user friendly a standard dual check valve can be used
|
Post Reply
|
Author:
hj (AZ)
NONE of those are approved for a system with heads ABOVE the BFP device.
|
Post Reply
|
Author:
bsipps (PA)
Perhaps I misinterpreted the ops plan
He plans to run a 1” main up to a high point then install a backflow device, from there run piping to the heads or using an irrigation hose which are planned to be below the actual device in which case all of the fire mentioned devices will work
|
Post Reply
|
Author:
Curly (CA)
As a general rule in California a reduced pressure device (rpd) is required for irrigation.
It can be located above or below irrigation system.
Device should be tested once a year by a licensed tester.
|
Post Reply
|
Author:
bsipps (PA)
Agreed but around here all testable devices and assemblies are required to be tested annually and results submitted to the water company not required by the township who’s minimum standard is just a non testable dual check valve
The op being on a well is not subject to any penalty by not testing in which case a non testable device can be installed
Rpzs are normally installed within the residence most outdoor testable devices are of a vacuum breaker type because they are easier to winterize
All that said having a testable device is better peace of mind as you know whether it is working or not
|
Post Reply
|
Author:
steve (CA)
Unless there's a local amendment, this is the 2019 CA Plumbing Code section -
|
Post Reply
|
Author:
hj (AZ)
IF I understand correctly, that is what someone suggested, NOT What he originally planned to do.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|