Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
Roan (CA)
I noticed slow leak in my temp/pressure valve on my water heater. When I tried to figure out why I tested my house pressure and it was at 95 psi. I checked the thermal expansion tank and it was bad. After getting the new tank I tested the water pressure after I drained the water heater to set the new expansion tank bladder (thought thermal expansion could have been the issue for the increased pressure), but at the hose bib and the cold water washer line I was still getting 95 psi. So now I think I had a couple problems, but the pressure might be from a bad regulator.
After trying to adjust my pressure regulator, the water pressure at the faucet will eventually slow, but every time I turn the faucet on it will come out with high pressure for about 5 seconds and then the flow will drop down to what I am assuming I turned the regulator down to. When I test the pressure, I get about 95 and when I turn a faucet on it will drop considerably, down to like 40psi. My question is, is my regulator bad or do I have another issue. I thought it would stop working and the pressure would either be low if it was clogged or it would fail and my pressure would match the city supply, the fact that it always starts high then reduces within a few seconds has me unsure.
The current model regulator I have is a Watts 25AUB DU-LF-Z3.
Thanks
|
Post Reply
|
Author:
steve (CA)
Do you know what the city pressure is? I think the regulator needs replacement/service.
|
Post Reply
|
Author:
Lorensr (CA)
The rubber kit in the r gulator is probably bad...cracked rubber maybe. Replace the rubber it should be good to go of the seat has not wired.
|
Post Reply
|
Author:
bernabeu (SC)
"....not wired."
wire drawn = eroded from excessive velocity
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
packy (MA)
yeah, the tank won;t lower the pressure it will absorb any excess pressure.
your problem is with the pressure regulator.
|
Post Reply
|
Author:
bsipps (PA)
Correct the prv should not allow the pressure to exceed 75 psi
They are cheap enough to just replace it
|
Post Reply
|
Author:
Lorensr (CA)
I stand corrected. Thanks Bern
|
Post Reply
|
Author:
bernabeu (SC)
... the nit has been picked AND split
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|