Welcome to Plbg.com and PlumbingForum.com. The best online (strictly) PLUMBING advice, help, dyi, and informational plumbing forum. Questions and discussions about toilets, sinks, faucets, drainage, venting, water heating, showers, pumps, water quality, and other exclusively PLUMBING related issues. Please refrain from asking where to purchase a product, or business, pricing, or legal questions, or for contractor referrals, or any questions not related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups. We do not sell your information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Narrowing a vent pipe then taking it back to its original size
Author: Panic521 (VA)

I have a 3" primary vent pipe that runs from the sewer connection through the roof. Unfortunately, I have a gambrel roof and when the pipe gets to where the slope of the roof changes it no longer fits behind the wall. Whoever built the house "solved" this problem by boxing in that area (about 1 cubic foot) which is pretty darn ugly. I'd like to put a 1 1/2" wye below the problem point and run two 1 1/2" pipes up into the attic. 1 1/2" pipe will clear the gambrel bend. In the attic, I can then invert a second wye and connect the 1 1/2" pipes to the 3" pipe so it can continue on its merry way. Essentially, I'm not changing the amount of fluid that the stack can support, I'm just changing it's pathway. By the way, I'm a newbie to anything more complicated than hooking up a sink and connecting a toilet. I'd appreciate any comments you may provide.

Post Reply

 Re: Narrowing a vent pipe then taking it back to its original size
Author: LI Guy (IN)

If you recall from math class, the area of a circle is the radius squared multiplied by pi. So for a 3" diameter pipe, the area of a cross section is the radius (1.5"winking smiley squared, multiplied by 3.14 = 7.07 sq in.

On a 1-1/2" pipe the area is 1.77 sq in, and two 1-1/2" pipes together have a cross section of 3.53 sq in.

so two 1-1/2" pipes can carry about half the air or water than a what a 3" pipe can carry (assuming same pressure and temperature).

The math says you would need four 1-1/2 pipes to match the volume of one 3". From a practical standpoint, it would probably work fine, but not sure if this type of thing is allowed by code, so will let the pros weigh in here.

- - - - - - -

Not a plumber by trade but a fierce DIYer

Post Reply

 Re: Narrowing a vent pipe then taking it back to its original size
Author: sum (FL)

If you have a 3" vent through the roof and if you have a blockage in your line inside the house and a plumber can't find a cleanout, he may go up to the roof to run a snake down. He will never expect that 3" vent will split into two or four 1.5" pipes and his full size auger head will be stuck 12 inches down. I think it's a bad idea because it messes with the serviceability of that pipe.

Post Reply

 Re: Narrowing a vent pipe then taking it back to its original size
Author: bernabeu (SC)

that type of thing is NOT, repeat NOT, allowed by code

- - - -

Retired U.A. Local 1 & 638
"Measure Twice & Cut Once"

Post Reply

 Re: Narrowing a vent pipe then taking it back to its original size
Author: jblanche (WI)

Can you add swing joints to change the slope?

*******************************
Links to the State of Wisconsin Plumbing Code:
[docs.legis.wisconsin.gov]
*******************************
I am not a plumber.
*******************************

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2021 Plbg.com. All Rights Reserved.