Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Is this mockup suitable for a basement bathroom (under concrete)?
Author: krivalsi (NY)

[@#$%&[postimg.cc]][/url]

I am doing a basement bathroom (shower, toilet and sink -> sewage ejector pit).
Here is a picture of a non-glued mockup of what I was planning to install under the concrete.
Any and all comments welcome.

Many thanks the folks on this site who have already addressed my previous mistakes and answered my questions.

I live in New York and I believe that means IPC for the inspection.

thanks in advance....Ken

Post Reply

 Re: Is this mockup suitable for a basement bathroom (under concrete)?
Author: hj (AZ)

Your Y for the toilet vent is backwards

Post Reply

 Re: Is this mockup suitable for a basement bathroom (under concrete)?
Author: bsipps (PA)

If those are the actual branch distances my code says the toilet does not have to be vented, you will need a vent where your end of the line cleanout is, and no pipe smaller than 2" should be underground

Post Reply

 Re: Is this mockup suitable for a basement bathroom (under concrete)?
Author: krivalsi (NY)

Thank you.

Post Reply

 Re: Is this mockup suitable for a basement bathroom (under concrete)?
Author: krivalsi (NY)

Thanks for your response.

>>> If those are the actual branch distances my code says the toilet does not have to be vented
Sorry, those are the pipe ID sizes. The total bathroom is 8.5' long and 5' wide.
So, I can remove the toilet vent and the toilet would be wet vented??

>>> you will need a vent where your end of the line cleanout is
I don't understand. Are you saying a vent by the cleanout OR a vent by the sewage ejector pit?
If you are referring to the sewage ejector pit end.....then, I agree and am planning to vent that in a new 2" vent pipe vertical into the attic where it will join an existing vent just before exiting the roof.

>>> and no pipe smaller than 2" should be underground
Everything here is 2" or greater except for the sink 1.5" p-trap (not shown).

- Ken

Post Reply

 Re: Is this mockup suitable for a basement bathroom (under concrete)?
Author: bsipps (PA)

If the toilet branch is within 8' off the main you do not have to vent it, a vent 3" vent at the end of the line to open air will work just make sure the penetration is 10' away from any windows

Post Reply

 Thank you clap
Author: krivalsi (NY)

Thank you.....Ken



Edited 1 times.

Post Reply

 Re: Basement bathroom
Author: packy (MA)

this is how i would do it.
forget the cleanout. you will never use it.
run 3 inch to the toilet and all else will be 2 inch.
use the toilet vent to drain the shower and the lav.
classic wet vent set up..

the 2 inch Y must be within 6 feet of the shower trap



Edited 1 times.

Post Reply

 Re: Is this mockup suitable for a basement bathroom (under concrete)?
Author: Ciel2333 (FL)

Make sure the drainage system will below the bathroom fixtures so that they can drain well. Here are some more info of building bathroom in the basement.



Edited 1 times.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.