Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
bsipps (PA)
Can I use compression fittings on oxygen lines or is brazed the only way to go
|
Post Reply
|
Author:
bernabeu (SC)
silver brazed is the ONLY way
nitrogen or argon purge
NO FLUX ALLOWED
oxygen piping is an art form unto itself -- have you seen an oxygen fueled fire? -- pray you never see one
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
bsipps (PA)
Thanks bern I was pretty sure that was the answer I like this forum more everyday
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
ps. just in case you have actually found an oxygen PIPING DISTRIBUTION system containing a compression fitting
CALL THE LOCAL FIRE DEPARTMENT RIGHT NOW
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
bsipps (PA)
Brass fittings are not combustible what's so bad about using them on a low pressure system like O2 yet copper is ok, just wondering
|
Post Reply
|
Author:
bernabeu (SC)
a compression fitting is a mechanical joint
said joint is weaker than the material(s) being joined
said joint "may" deform and weaken the material(s) being joined without visible indication or ability to test for said deformation
said joint "may" be subject to vibration failure - ANY leakage on oxygen service piping could/would be a catastrophic failure
Albeit oxygen distribution is SUPPOSED and DESIGNED to be low pressure the piping system itself MUST be constructed to allow for 100% leak free if there should be a regulator failure or other mishap.
a silver brazed joint is STRONGER than the base copper
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
bsipps (PA)
Understood thank you
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: