Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
bpatton (GA)
Been dealing with issue for 3 or 4 years. Shower (on a septic system) starts smelling bad within 5 seconds of using it. It has a P trap and a guy just installed a studor vent about 2 feet downstream of the trap...that seemed to help a little but not sure. The smell stops after the shower is off...after 10 minutes or so. Please help
|
Post Reply
|
Author:
packy (MA)
a studor vent only allows air to enter the system.
you have a positive pressure building up when you use the shower so a studor is useless.
temporarily remove the studor to see if the smell comes out that open pipe rather than backing up into the shower.
so if removing the studor allows the smell out then you need a proper vent pipe to let the foul air go to the atmosphere.
a cigarette or a smoldering piece of cardboard held over the open pipe will tell you what is happening.
may have to experiment a couple of times with water not running and then with water running.
|
Post Reply
|
Author:
bpatton (GA)
Thx for your help. I have a vent through the roof that i could tie it into. It's about 12 - 15 feet from it horizontally. Will that work?
|
Post Reply
|
Author:
packy (MA)
do the testing i suggested before making any more changes.
i could be wrong in my assessment of the situation. (i'm not infallible).
to answer you question, the vent could be run the 12 feet but there are certain criteria that must be met.
the main one is the vent can tie in to an existing vent but it can not tie in below the flood rim of any fixture being served by that vent.
so its not all that technical to understand but take one step at a time.
if running the vent is needed then a picture or two will help.
|
Post Reply
|
Author:
NP16 (OR)
when's the last time you have the septic serviced?
|
Post Reply
|
Author:
sharp1 (IL)
Since you have a septic system, do you also have well water? What happens if you just run cold water in the shower? Some well water reacts with the anode rod in a water heater causing a sulfur type smell, cold water would not have the odor.
|
Post Reply
|
Author:
bruceb3 (MI)
Good catch, Sharp1. I didn't even think about well water. Yes, an anode rod can cause very foul odors with certain well water.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: