Welcome to Plbg.com
Thank you to all the plumbing professionals who offer their advice and expertise

Over 698,000 strictly plumbing related posts

Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 boiler not igniting automatically
Author: HoweDIY (CT)

Weil-MClain
CGM-25 Series 8

Woke up this morning to a cold house, after poking around a bit. I switched the lever on the High limit Control from Auto to Manual and the burners ignited right away.

I am hoping to get some insight.

What would cause it to stop igniting while on auto?

Why do the burners automatically ignite when this switch is in the Manual position?

is it dangerous to keep the system running in manual mode?

Thank you for the help.

Post Reply

 Re: boiler not igniting automatically
Author: Paul48 (CT)

Is there any other info about the high limit control that you can give us? Is there a Honeywell sticker on it? It sounds as though the boiler thinks the high limit has already been reached, and that's why it won't fire in auto. I'd like to be able to see what's going on with the H.L. control though, to be able to tell you more.

Post Reply

 Re: boiler not igniting automatically
Author: HoweDIY (CT)

Paul48, from all vantage points I cannot see a make of the High limit control. currently the high limit temp is set at 210 degrees F.

Post Reply

 Re: boiler not igniting automatically
Author: Paul48 (CT)

Low battery on the T-Stat? Put it back on Auto and jump the T-stat connections at the boiler.



Edited 1 times.

Post Reply

 Re: boiler not igniting automatically
Author: HoweDIY (CT)

Hello Paul48,

I have one battery operated T-stat and one which doesn't have a battery. The T-stat is not indicating a low battery... anyway. I do not know how to jump the connection, therefore I will contact a local service tech.

Post Reply

 Re: boiler not igniting automatically
Author: Palm329 (VA)

I believe to turn on the heat you would look at where the thermostat wire connects to the furnace. You will see the wires connecting to some screw-down terminals. Using a piece of wire to connect the red and white wires should turn on the heat regardless of the thermostats.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.