Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
Kay537 (MA)
On a new house construction, we have rainwater coming into the basement where the sewer pipe exits the concrete wall to the septic system. The plumber said he had to jackhammer the hole that the excavator had put in to make it larger in order to get a bigger fitting in there. The PVC elbow is partially cemented into the wall. Should the elbow joint be partially hidden, as it appears to be, in the concrete wall? And does the bend in this drain line look too tight? We are wondering why it is leaking and if the plumbing has been done correctly or not.
Here are two images:
[drive.google.com]
[drive.google.com]
Thank you
Edited 5 times.
|
Post Reply
|
Author:
bernabeu (SC)
good / best practice:
fitting NOT in wall
sleeve through/in wall cemented in TIGHT
pipe through sleeve to allow for any future settling of structure
sleeve/pipe caulked or packed with oakum (not cemented solid) to prevent water intrusion
if penetration 'area' is leaking something is wrong
best of luck
(others will 'chime in' re: code required MINIMUM standard)
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
packy (MA)
enlarging the hole a little bit will not weaken the wall.
as for the fitting being buried inside the wall, you had better have a discussion with the plumbing inspector about that.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: