Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
Marko1 (MO)
I was going to run pvc from h2o heater relief valve to drain line...is that ok? Or why not? (No floor drain) thanks...I have already run a.c. condensate line into drain, is that ok?
I know it should probably be cpvc rather than pvc but couldn't find in 1" dia. and figured a discharge would be rare and unlikely and if it happened would be a very short momentary burst rather than continual flow...
Edited 2 times.
|
Post Reply
|
Author:
hj (AZ)
1. You only need 3/4"
2. sometimes it is a long term continuous flow
3. If it is hot water it will melt the PVC
4. use copper or CPVC
|
Post Reply
|
Author:
NP16 (OR)
"I have already run a.c. condensate line into drain, is that ok?"
Did you provide an air gap?
|
Post Reply
|
Author:
bernabeu (SC)
For the T-PRV: a visible air gap AND a (receptor) pipe and trap sufficiently large to accept FULL FLOW of POTENTIAL discharge.
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
packy (MA)
strange but as restrictive as mass codes are, they just want the discharge left 12 inches above the floor.
enough to get a bucket under.
|
Post Reply
|
Author:
Marko1 (MO)
Uh oh .. apparently not since I don't know what that is
|
Post Reply
|
Author:
Marko1 (MO)
By air gap does that mean like a studer vent?
|
Post Reply
|
Author:
packy (MA)
i laymans terms...
an air gap just means a space between the discharge and the pipe you are connecting it to.
this prevents any bad water from backing up into the discharge.
|
Post Reply
|
Author:
hj (AZ)
It is not a big deal with a condensate drain, because you do NOT drink the water where it comes from.
|
Post Reply
|
Author:
Marko1 (MO)
Thanks to all you guys for your replies
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
it would take a very unique set of circumstances for a water heater discharge pipe to syphon water back into the potable water system..
|
Post Reply
|
Author:
bernabeu (SC)
the discharge of a T-PRV must be VISIBLE ~ may NOT be directly connected to a drain
even if run 'outside' the discharge MUST be visible
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Author:
packy (MA)
yeah, there's also something in the code about discharging water hotter than 180 into a sewer ??
|
Post Reply
|
Author:
hj (AZ)
And WHO has ever installed a cool down receptor for a water heater discharge line.
|
Post Reply
|
Author:
bernabeu (SC)
ME ME ME
I actually HAVE installed one.
Albeit it was called a 'heat-exchanger blow-down flash tank'.
Seriously!
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: