Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
SJP (MD)
Hi all, Is it acceptable to connect a Water Closet Flange directly to a 3" DWV Combination Wye & 1/8 Bend instead of connecting it to a Closet Bend or a 3" Long Sweep 90 ? Thanks
|
Post Reply
|
Author:
hj (AZ)
It depends on HOW you do it and whether you are venting it properly.
|
Post Reply
|
Author:
SJP (MD)
I will draw and try to attach a sketch.
|
Post Reply
|
Author:
packy (MA)
a dry vent like you show is going to plug up over the years.
you would be much better off if you could vent the toilet with a wye rolled up like this.
|
Post Reply
|
Author:
SJP (MD)
Thanks for the info and guidance.
Edited 1 times.
|
Post Reply
|
Author:
srloren (CA)
For a vent to work properly it should be above the drain flow line.
Edited 1 times.
|
Post Reply
|
Author:
SJP (MD)
Thanks, So the vent line works best when it is higher than the drain and not on the same lateral alignment?
Edited 1 times.
|
Post Reply
|
Author:
bernabeu (SC)
correct
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
sum (FL)
For dry vents right? If wet vents there is flow rinsing out the line then no roll up is necessary correct?
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
correct..
Edited 1 times.
|
Post Reply
|
Author:
Dunbar (KY)
Flat venting is your picture showing, and rolling vents under 42" without the use of continuous 45's will never allow the sludge to 'fall' back into the path of the waste line in a clogged moment. Has to be a 45 degree continuous rise.
Should 90 the water closet straight to your wall, turn up a tee and then come out of the tee with two 45's to get turned back in the direction of the high wall main cleanout. That way the toilet is vented properly.
- - - - - -
Everything in Plumbing can be repaired or replaced.
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: