Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Baseboard heat not working in half of the house
Author: Jbridge (NY)

I have been using my heat without problems for about 2 weeks. As of 4 days ago the heat would not get to the set temperature.At first I was goimg to change the thermostat but then resized that some baseboard pipes were getting hot while others were not.

I found the 2 relief valves and tried bleeding them, one the water came out hot the other the water came out room temperature I guess you would say. No air sound came out of either end.

The furnace does keep kicking on but only stays on for 2-3 min.

If water is coming out can air still be the system? The side that has the room temp water coming out when opening the valve should I keep bleeding it until hot water comes out?
Is it possible to remove to much water?

Post Reply

 Re: Baseboard heat not working in half of the house
Author: packy (MA)

can you post a picture of what you call the "relief valves" ?
just opening the valves does not remove any air.
and yes, you can remove too much water if the system can not replenish it fast enough.

Post Reply

 Re: Baseboard heat not working in half of the house
Author: Paul48 (CT)

Baseboards can be nearly impossible to bleed, unless the system is set up with valves in proper locations. You want to create flow in one direction, otherwise the water will take the path of least restriction and that may not be where the air is. In it's simplest, cheapest form, on a single loop system, you would have a ball valve on the supply and return at the boiler. You would then have a boiler drain on the system side of the supply and return. You close the valves to isolate the boiler. You run a hose from a sillcock to one boiler drain and run a hose from the other boiler drain out onto the lawn. If you have a split loop make sure you add an additional valve to force the flow through the split, then open it up....done. Next spring put a spirovent on the system to automatically remove air.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.