Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Replacing water line from meter to house
Author: Darkhog (WA)

Hello folks. I am having this work done, and would really appreciate a second opinion on some things.

I have a 3/4" water meter, now connected to 1" PEX (UPONOR AquaPEX PEX5106 SDR9)in a 1.5" ABS SCH 40 sleeve. I believe it is supposed to be buried at 24", but some places have more digging challenges than other, and in some places the top of the pipe to ground is closer to 18-20" when measured from top of abs. In one place maybe a little bit shallower. Is this something I should worry about? It has been a tough dig, so I don't want to harass them, but I do want this to last as long as possible.

Also, the PEX is mostly in the sleeve, but there are a few gaps. There is a foot at the start, and then 3 feet where it isn't as the pipe needs to bend a bit. Is that ok?

The ABS will be covered with sand, and then buried. Inspector comes out later today.

Thanks for the help!

Post Reply

 Re: Replacing water line from meter to house
Author: hj (AZ)

IF the inspector is happy with it, then there is nothing for you to worry about.

Post Reply

 Re: Replacing water line from meter to house
Author: Darkhog (WA)

Thanks for the response! Are there any questions I should ask the inspector?

Post Reply

 Re: Replacing water line from meter to house
Author: hj (AZ)

No, he will get along just fine without you being there.

Post Reply

 Re: Replacing water line from meter to house
Author: NP16 (OR)

any piping installed less than 24" can be insulated.

Post Reply

 Re: Replacing water line from meter to house
Author: hj (AZ)

"insulation" will not help. Plastic has to be buried deep to protect it from digging damage, NOT temperature.

Post Reply

 Re: Replacing water line from meter to house
Author: bernabeu (SC)

Quote

..... Also, the PEX is mostly in the sleeve, but there are a few gaps. There is a foot at the start, and then 3 feet where it isn't as the pipe needs to bend a bit. Is that ok? .....



No, it is NOT O.K.

While it may, or may not, comply with the code MINIMUM it is NOT good practice.

If the pipe needed to be bent a bit then the pipe should have been bent a bit.

'pic' is PVC but the same principle applies to ANY pipe or tubing (fill with sand, heat, bend, dump sand)




==============================================

"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638

Post Reply

 Re: Replacing water line from meter to house
Author: Darkhog (WA)

Thanks. In our area, the sleeve isn't required by code. The inspector thought it was excellent work. With respect to the exposed PEX pipe, he just said to be sure it has plenty of sand around it. The sand is required and protects against rocks that could rupture the pipe.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.