Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
gtg (OK)
Hello, great forum!
I installed our tub drain vent wrong. Drain, vent, p-trap. I keep reading about a p-trap being able to use another vent that is less than 6' away. Am I okay to leave incorrect vent in place and rely on the vent 4'8" away?
Both tub drains are 1.5" and enlarge to 2"
[@#$%&[smg.photobucket.com]][/URL]
Edited 4 times.
|
Post Reply
|
Author:
packy (MA)
if i am reading your drawing correctly, the tub is wet vented. the vent/drain should be 2 inch but it will work OK.
|
Post Reply
|
Author:
Palm329 (VA)
What’s your slope on that 1.5” pipe? Or, in other words, what’s the height difference in inches between the trap and where it meets the Y fitting to the correctly vented branch?
|
Post Reply
|
Author:
hj (AZ)
The way he describes it the waste and overflow is VENTED, not the trap, and if it is connected TO an "active vent" the odors will be drawn into the room. In other words, the other vent may or may not be effective, but THIS one has to be disconnected.
|
Post Reply
|
Author:
LI Guy (IN)
What drawing?
- - - - - - -
Not a plumber by trade but a fierce DIYer
|
Post Reply
|
Author:
hj (AZ)
no drawing. He said "drain, vent, P trap, which means the vent is for the w&o, NOT the trap.
|
Post Reply
|
Author:
packy (MA)
there was a drawing but one of his 'edits' must have taken it away..
|
Post Reply
|
Author:
Palm329 (VA)
There was a drawing yesterday that showed an “incorrect” vent connected to the tub drain prior to the actual trap, rather than after the trap. As Hj said, if that incorrect trap connects to a vent branch let’s say in the attic rather than runs independently thru the roof, it could allow sewer gas directly up the bathtub drain.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|