Welcome to Plbg.com (also known as PlumbingForum.com) where plumbing advice, education, information, help and suggestions are provided by some of the most experienced plumbers and plumbing contractors anywhere who all wish to "give back" to society. Since 1996 we have been free without popup or other invasive ads and known to be the best online STRICTLY PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to find and/or purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't track you. We absolutely do not sell your personal information. We are made possible by:
Author:
birddoggiest (ID)
I am working on a restaurant remodel and the dishwasher waste is indirect. I can't find in the UPC where the code is for this. I thought they were normally direct connect. Am I worng?
|
Post Reply
|
Author:
dlh (TX)
i have always done them indirect. usually everything in a kitchen is indirect with the exception of disposers and those do not go to the grease line they go to the sewer
- - - - - - -
PLUMBERS "Protecting The Health Of The Nation"
|
Post Reply
|
Author:
LemonPlumber (FL)
I think it depends on if the machine has a built in air gap or not.Good Luck.
|
Post Reply
|
Author:
dlh (TX)
also remember pvc is not rated for hot water so can not be used for the drain piping. either galvy, copper, or cpvc are supposed to be used
- - - - - - -
PLUMBERS "Protecting The Health Of The Nation"
|
Post Reply
|
Author:
Wheelchair (IL)
Commercial Dishwashers, are big generators of grease from the wash cycle. In direct thru a separator is most important.
Best Wishes
|
Post Reply
|
Author:
Krazyfx (MD)
As far as the dishwasher discharge, floor sinks are commonly used, which in turn are indirect connection. Depending on the available floors sinks being a rehab, you could discharge the dishwasher into a main drain as long as it is trapped and after you verify that line is a grease trap line and not a sewer connection.
Edited 1 times.
|
Post Reply
|
Author:
redwood (CT)
And I would say you may want to disregard krazy's answer as it may only apply in Maryland.
- - - - - - - - - - - - - - - - - - - -
Since 1995 (3 years before Google started) PlumbingSupply.com has been THE best plumbing supplier on the web. Please visit our sponsor [www.PlumbingSupply.com]
|
Post Reply
|
Author:
dlh (TX)
ok so i forgot the by the codes used in my area disclaimer.
my bad
- - - - - - -
PLUMBERS "Protecting The Health Of The Nation"
|
Post Reply
|
Author:
Pipewrench (CA)
What wrong about discharging and dishwasher directly? I would also assume it should be tied into the grease line not sewer, because its a commercial kitchen, and you can't control what is put in them. Same goes for hand sinks and such in the kitchen areas. Am I missing something?
|
Post Reply
|
Author:
dlh (TX)
it is a health issue. commercial kitchens are not residential kitchens. their health standard is way above residential since they deal with a large amount of the public. connecting it directly opens it to being contaminated if something should go wrong in the line.
and then where people are getting tieing them into anything other than a grease line i think was brought up by me just mentioning that everything in the kitchen is normally indirect with the exception of the disposal which around here is to be tied into the sewer since the food causes problems with the grease interceptors
- - - - - - -
PLUMBERS "Protecting The Health Of The Nation"
|
Post Reply
|
Author:
Pipewrench (CA)
I thought disposers are supposed to run through a seperator then into the interceptor, as far as the UPC states. The health issues makes sense.
|
Post Reply
|
Author:
dlh (TX)
ah that is just some areas adding to the code.
ipc section 413.3 commercial food waste grinder waste outlets.
commercial food waste grinders shall be connected to a drain a minimum of 2 inches in diameter. commercial food waste grinders shall be connected and trapped separately from any other fixtures or sink compartments.
localities can add to that and is what you are talking about.
i dont have the upc with me right now or i would look that one up to see what it says
- - - - - - -
PLUMBERS "Protecting The Health Of The Nation"
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|