Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
packy (MA)
the trap for the tub needs to be below the drain line. what you have now is a full 's' trap and will syphon whether you have a vent or not..
continue your trench all the way to the wall beside the tub and put the studor vent in that wall behind an access panel.
|
Post Reply
|
Author:
fcat (VA)
Thanks for the info, yeah that's just my poor drawing on the trap, it will be the correct one
If there's away without using that end wall it would be preferred, that walls going to be fully tiled whereas the partition wall I'm building and hoping to use I'll be able to have the access panel in the side that isn't in the bathroom as it will be just drywall and i can put an access panel in and it will be covered by furniture.
Can something like this work ?
|
Post Reply
|
Author:
packy (MA)
the drawing with 'less thsn 5 ft' written on it will be good.
use a 'y' for the vent connection not a tee.
the studor vent will have a threaded end so it will screw into a female adapter.
also. 2 inch pipe is the minimum size allowed underground so you will need a 2 inch sanitary tee to tie into the existing drain.
|
Post Reply
|
Author:
fcat (VA)
Thanks for the info Packy! appreciate it
Coule of questions:
1. Am i right in thinking the Studor vent does NOT have to be above the flood rim ?
2. I'll use a Santee at the junction into the existing 2" drain, a sweeping 90' at the 90' bend and then a santee put in backwards or a Y to go upto to the vertical for the studor , is that correct ?
|
Post Reply
|
Author:
fcat (VA)
This setup look ok ?
ill then go into a Santee at the 2" drain (not in the picture) and come up vertical with a studor vent into the partition.
|
Post Reply
|
Author:
packy (MA)
it is about as good as you are going to get...
|
Post Reply
|
Author:
steve (CA)
Turn the combo tee 180*.
|
Post Reply
|
Author:
fcat (VA)
Got it ,thanks This might be a stupid question but when i get through the concrete to get the the 2" drain, how can i cut the pipe to insert the santee if the pipes are rigid with no movement ? the bottom part with be in the soil, the top part is in the wood plate and studs!
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
the fitting to use is called a 'slip' coupling. it is simply a coupling that is smooth inside (no stop in the middle).
only problem is you have to work quickly or the glue sets up with fittings in the wrong orientation.
|
Post Reply
|
Author:
fcat (VA)
Thanks,got a couple today.
|
Post Reply
|
Author:
fcat (VA)
How the hell do you get these slip fittings to work!!
When you add all the glues then slide the fitting up it takes all the glue up to the top half and leaves hardly any for the bottom half! Ive done this twice now and both times the fitting has leaked from the bottom!
Am i allowed to use a Fernco rubber coupling out of the ground?
|
Post Reply
|
Author:
steve (CA)
Use a shielded coupling.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|