Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
Pipe runner (AZ)
looked at a job today where the homeowner wants to add a toilet upstairs. The best route would require drilling through 1 or 2 ceiling joists that are 9" wide.
so by the code max hole size would be 3" (1/3 of width) and the 3 1/2 hole I need to run 3" ABS is too big and a code violation.
Anyway structural way around this if an carpenter came in and added material?
I'm thinking the drain will have to run parallel to the joists and come down a different wall or below the joists in the ceiling below.
any input is always appreciated. thanks.
Edited 1 times.
|
Post Reply
|
Author:
North Carolina Plumber (NC)
Plywood can be glued and screwed to the side of the joist(s) to strengthen them. How long are the joists ? On 16" centers ?
|
Post Reply
|
Author:
PlumberManDan (IA)
I generally try to get the homeowner to go with a soffit, makes your life much easier and in many cases it can accentuate a room because lighting can be placed in there also. Most are open to the idea from my experience since it is going to cost them less in the long run.
PlumbCat TM 2003
Plumbermandan
|
Post Reply
|
Author:
packy (MA)
how far from the end will the holes be?
if you are within 2-3 feet from the end, i forget which, they want the joist notched rather than drilled in the center.. something about stress vs compression..
|
Post Reply
|
Author:
Ridgidman (VA)
Another option that the plumbing code talks about is the use of metal stud shoes. Sometimes the building inspector will allow these to be used if the hole size exceeds one third of the total joist depth.
|
Post Reply
|
Author:
hj (AZ)
The ideal would be to put it between the joists and then drop down in a wall, an alternative would be to header off the joists to create a "box" for the piping.
|
Post Reply
|
Author:
Pipe runner (AZ)
all good solutions. thanks so much.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: