Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 changing cast iron boiler pipes on furnace
Author: Trevor V (NY)

Have the old hot water/boiler system to heat my 1955 house. Water circulation by electric pump. Oil/electric to heat the water. I want to change part of the supply pipe to the radiators that is visible in a room in the basement.

Is PEX tubing good for hot water furnace applications ? The main supply now to the heaters upstairs is 1 1/4 OD cast iron pipe. I want to change/merge cast iron to PEX.

Also, do the old cast iron "T's that connect to the pipes leading to the heaters upstairs have any sort of water deflectors inside to send the water into the heater upstairs ? Will a PEX "T" work as well to send the water up into the radiator ? Need advice !!!

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: hj (AZ)

To answer your last question first. If they are "Mono-flo" tees they DO have "deflectors" and if you eliminate them the system will NOT work properly.

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: Paul48 (CT)

If they are tee'd off a main, there is something in them to divert the water.

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: stuckinlodi (MO)

Here's a cutaway drawing of one style showing the deflector/diverter "bump" inside:





Edited 2 times.

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: packy (MA)

usually there are two tees to each radiator. one is a monoflo or scoop tee while the other is a regular tee.
you can use a pex tee for the standard tee but not for the scoop tee.
but, you do have to be careful to not reduce the size of the main pipe by putting in a smaller pex tee.

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: Don411 (IN)

Interesting note, I have the same setup (although I replaced oil with gas), but there are 2 heating loops that run around the basement, one supply and the other return. Each cast iron radiator is plumbed to the supply side and the return side. Same setup with 1-1/4" iron pipe with the diverter tees on the supply side.

The radiator in the kitchen was moved at some point, and the original pipes going to it were cut, although they left the original tees in the supply/return loops. The pipes going to the radiator were reduced with fittings to 1/2" copper, which seems like it would starve that radiator, but that one gives off more heat than any other radiator in the house!!

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: hj (AZ)

Two pipe systems do not NEED diversion tees, because the flow to the radiators can be accomplished with changes in pipe size. In face, a diversion tee could be detrimental, because the diverted flow does NOT return to the same main the way it does with a one pipe system.

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: packy (MA)

any old cast iron monoflo tees i have seen were true monoflo. they had that funnel shaped diverter inside rather than an angle piece that acts like a scoop.

Post Reply

 Thanks for the info :thumb
Author: Trevor V (NY)

Thanks for the info on mono flo T's from PEX. That is what I was looking for. Will look for them before starting my project. Are these T's easy to find in store or only at dedicated plumbing shops ?



Edited 1 times.

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: Trevor V (NY)

I would be running a one inch PEX tubing for the supply line. So far have not found a one inch diameter monoflo T on the net. Seems 3/4 is the max size. Do not want to reduce the flow at the T's. Are there one inch monoflo T's available ?

Post Reply

 Re: changing cast iron boiler pipes on furnace
Author: packy (MA)

lots of them out there.. [#$%&.com]
they also come in cast iron threaded so you don't have to solder. just screw in adapters. but these are harder to find..

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.