Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 New basement bathroom venting
Author: Samtrav (MD)

I'm looking to install a new bathroom in my basement and a local plumber told me I can connect everything (sink,toilet,shower)to the main stack within 5-6 ft and I would not need to add a vent as the main waste stack would act as one. Is this true (also idk of it would help but 2 ft above where I would tie in the new bathroom is the drain line for the kitchen sink which is directly vented to roof without anything else above it) option 2 would be to cut into the sink drain earlier bring it underground enlarge to 3 in make all my connections and then tie into main stack. Do either of these work



Edited 1 times.

Post Reply

 Re: New basement bathroom
Author: hj (AZ)

BOTH of those pipes are DRAINS, NOT vents, so they CANNOT be used as vents. And as far as what he told you about the distance from the main drain riser, it is FALSE, except for some special situations which I doubt apply to your installation. How long has he been a "plumber"?

Post Reply

 Re: New basement bathroom
Author: Samtrav (MD)

No idea it's a friend of a friend situation-which is why I wanted to double check here. Why wouldn't option 2 be a valid wet vent?

Post Reply

 Re: New basement bathroom
Author: North Carolina Plumber (NC)

You can't wet vent fixtures on a different floor levels. I assume the kitchen is on the 1st floor ?

Post Reply

 Re: New basement bathroom
Author: steve (CA)

All fixtures in the wet vent system need to be on the same floor level. Any drain piping coming from the floor above can't be used as a vent for fixtures on a lower level.

Post Reply

 Re: New basement bathroom
Author: hj (AZ)

Because it is NOT on the same floor level as the sink. Which is also why an AAV is a bad idea for a lower level fixture.



Edited 1 times.

Post Reply

 Re: New basement bathroom
Author: Samtrav (MD)

To properly run a vent would require ripping out the walls on first and second floor and a bit of ceiling (the walls don't line up anywhere on the side of the house) including jumping 2 or 3 joist bays. Would I be able to use an AAV to avoid the expense/time/mess. I know plumbers don't like using them but is that a pesonal preference/the way things were always done like pex vs copper or are there potential functional issues in a normal installation? Is it just a matter of the AAV failing and if I smell sewer gas open a window and replace the valve?



Edited 1 times.

Post Reply

 Re: New basement bathroom
Author: North Carolina Plumber (NC)

Our code does allow the use of an AAV for a basement bath, just get it as high as you can, leave access to it, and be sure it can get plenty of air flow. If it's going to have to be in a wall, don't insulate around it and use a louvered grill over the opening in the sheetrock where it is.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.