Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
jayperl (NY)
Two Zone Hydronic system. Zone 2 (2nd floor) not getting hot. Bled the system. Pressure is 20psi hot. Temp 190F. 1st floor no problem. Taco 007 shows .8A just like zone 1. Pumps are on return. Pipe after check valve for zone 2 is hot, return is cold. Any idea?
Anyway to show a pic here?
Josh
|
Post Reply
|
Author:
packy (MA)
[www.plbg.com]
the problem could be the circulator or it could be air..
post a picture...
|
Post Reply
|
Author:
Paul48 (CT)
Baseboard type emitters can be near impossible to purge air from by just opening a bleeder on the baseboard. With any type of emitter, it's best to set the system up with valves so you can create flow in one direction.
|
Post Reply
|
Author:
jayperl (NY)
I was bleeding it from the return line of that zone near the boiler.
|
Post Reply
|
Author:
Paul48 (CT)
Ok.....as long as you were able to close a valve and create flow in one direction. What is the pressure of the system?
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
as paul says, create a flow in one direction..
so, shut off a valve below the hose valve you are bleeding with. then open the hose valve.
what you have to do is put the end of the hose into a bucket and look for air bubbles. if there are bubbles coming out, you need to keep running until the water runs clear with no bubbles.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: