Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
kjpyatt (MO)
I'm wanting to add a utility sink in my basement. 9 feet from the sink is the vertical 3 inch PVC drain pipe (home built 2001). I'd like to put the sanitary tee there and wonder if by the international code I need to vent the sink separately. About 4 feet up from basement foundation, the 3 inch pipe has a clean out and is reduced to a 2 inch pipe. the 2 inch pipe then goes up three more feet to a wye - the wye goes straight up to the 1st floor for the kitchen sink and dishwasher at 1-1/2". The branch out from the wye stays at 2 inches and goes up to the 2nd for for the master shower and bath.
It seems like that is enough to use as a wet vent but I would love advice... Code!
I have pictures but I don't see a way to post them on this forum.
|
Post Reply
|
Author:
North Carolina Plumber (NC)
If the 3" pipe you are teeing into has waste draining down from above, then the sink will have to be vented. You can't wet vent a fixture with one on another floor level.
|
Post Reply
|
Author:
packy (MA)
if an AAV (studor vent) is allowed in your area, that would work..
|
Post Reply
|
Author:
kjpyatt (MO)
If by "waste" you mean toilet, then no it doesn't. It has a kitchen sink and dishwasher I the 1.5 inch, a shower and a tub on the 2 inch.
|
Post Reply
|
Author:
kjpyatt (MO)
We use the 2009 International Plumbing Code... which... As a software engineer that specializes is database technology, finding details on code is unnecessarily difficult in this age of technology. It's a shame.
|
Post Reply
|
Author:
steve (CA)
Any water coming from the floor above prevents you using the stack as a wet vent.
|
Post Reply
|
Author:
kjpyatt (MO)
"Any water coming from the floor above prevents you using the stack as a wet vent".
Really? Isn't that the very concept of a "wet vent"? Maybe I CA wet venting isn't allowed at all - wouldn't surprise me at all when it comes to CA and it's over-regulation.
|
Post Reply
|
Author:
packy (MA)
MA wet venting has the same restriction. no wet venting from floor to floor.
maybe has something to do with the speed the water is falling and the amount of air pressure it creates as it moves down a longer pipe??
|
Post Reply
|
Author:
kjpyatt (MO)
Ah, floor to floor. That might be the kicker. I'll keep looking into code if it's possible to find it.
|
Post Reply
|
Author:
steve (CA)
2009 IPC
909.1.1 Vertical wet vent permitted. Any combination of
fixtures within two bathroom groups located on the same
floor level is permitted to be vented by a vertical wet vent.
The vertical wet vent shall be considered the vent for the fix-
tures and shall extend from the connection of the dry vent
down to the lowest fixture drain connection. Each
wet-vented fixture shall connect independently to the verti-
cal wet vent. Water closet drains shall connect at the same
elevation. Other fixture drains shall connect above or at the
same elevation as the water closet fixture drains. The dry-
vent connection to the vertical wet vent shall be an individ-
ual or common vent serving one or two fixtures .
|
Post Reply
|
Author:
kjpyatt (MO)
Thank you, Steve.
This part "Each
wet-vented fixture shall connect independently to the verti-
cal wet vent" seems to be what the plumber I ran into at the store said. He said since it's about a 9 foot run to my sink, I should vent close to the sink, and go up then back over to the 2" section between the wye at the top and the 3 inch section below it. I've got about 4 ft of 3 inch, the cleanout, then about 3 ft of 2 inch before it splits.
That's are no "water closets" in that run.
Edited 1 times.
|
Post Reply
|
Author:
steve (CA)
According to IPC, only bathroom fixtures can be wet vented and NO fixtures from a floor above can drain into the wet vent.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|