Welcome to Plbg.com
Thank you to all the plumbing professionals who offer their advice and expertise

Over 698,000 strictly plumbing related posts

Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 Taco zone valve relacement
Author: mountainfarm2012 (NH)

After replacing one of the Taco zone valves,and purging the air, my heat is up and running fine my hot water was hot but now isnt staying hot.. i have a boiler and boiler mate.. I tried purging the air again to the hot water lines the lines gets hot for a while then cools off and no hot water..

Post Reply

 Re: Taco zone valve relacement
Author: North Carolina Plumber (NC)

Is the zone valve you replaced for the Boilermate ? What happens when the temp cools down in the Boilermate ? Does the zone valve open ? Does the circulator pump turn on ? Does the boiler fire ?
Since the problem just started it's probably related to the wiring, did you wire the end switches together ?

Post Reply

 Re: Taco zone valve relacement
Author: mountainfarm2012 (NH)

zone valve was for heating for 1st floor heating which is working fine..boiler working fine...just no hot water in faucets or showers, pipes to boilermate will get hot after purging but then cool off after a while and no hot water

Post Reply

 Re: Taco zone valve relacement
Author: North Carolina Plumber (NC)

Is the zone valve open to the boilermate ? Since the water has cooled, the zone valve should be open, the end switch should be making contact and the circulator pump should be running. If all of the above are true then you sill have a pocket of air trapped in the piping.

Post Reply

 Re: Taco zone valve relacement
Author: Paul48 (CT)

If the boiler-mate is cold, the boiler should be firing constantly. If a zone valve is used, the end switch may not be made, and will hold the boiler out. Or, the aquastat on the boiler-mate is not calling for heat. Or, if a zone valve control w/priority domestic hot water is used, it could be faulty. We need more info, or pictures taken from far enough back to be able to see everything.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.