Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
JeffT (NJ)
I have this idea to solve the dilemma of hot water delay vs. volume.
I have a bathroom (sink, toilet, bath/shower) a long way from the water heater. I'll run 3/4" pex for the cold. I'm thinking of running two 1/2" hot lines; one will normally feed the sink, the other will only feed the shower/tub.
But what if I allow the shower/tub to draw from the sink hot line as well? I'll put a check valve between the hot lines that keeps the sink from drawing from the shower/tub feed.
Won't that give me fastest possible hot water for the sink and high hot water volume for showering and filling the tub?
Please debunk this idea before I try it!
Thanks!
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
interesting idea..
i would think that the resistance of the check valve (even though it is facing the correct direction) might not allow very much water to cross over? but then again i'm only guessing????
|
Post Reply
|
Author:
North Carolina Plumber (NC)
If your shower valve was 3/4" and you used a swing check valve you would probably be on track. The openings in your 1/2"shower valve is probably no more than 3/8" so I don't think you'll notice any increase of volume by using two 1/2" pipes.
|
Post Reply
|
Author:
m & m (MD)
Insulate both of them.
|
Post Reply
|
Author:
JeffT (NJ)
Thanks all for your responses. Will, indeed, insulate both.
Regarding fixture inlet sizes I'm thinking of using some high flow fixtures so I'm guessing they won't be much restricted from full 1/2 Cu I.D. I'm trying to address the difference from the .485" I.D. on the 1/2" pex vs. .545" I.D. on the 1/2 Cu.
Edited 1 times.
|
Post Reply
|
Author:
sharp1 (IL)
If 2 water lines are feeding the same valve equally it will take 2x as long to get hot water to the valve. If unequal feed, one line will have hot and the slower line will still be flowing cold water. A separate 1/2" pex line to each valve will get hot water faster than a 3/4" feeding both. Assuming you have a standard shower valve with 1/2" connections.
|
Post Reply
|
Author:
steve_g (CA)
I feel like I'm missing something here. If you're going to run 2 hot lines to one bathroom, use one as a return to recirculate the hot water. Put a small recirc pump & check valve on it. That would be the fastest way to get hot water to the bathroom.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|