Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
roundrightfarm (WV)
I have a situation where 3 bathrooms (one first floor and two second floor) each have their own vents (each 2" common vented toilet & sink) which will terminate near each other up in the attic. Is it a problem to combine these vents into a single one for the roof penetration? I would still have more total vent area going through the roof than septic pipe area.
|
Post Reply
|
Author:
packy (MA)
sure... combine all into a single 3 inch thru the roof.
my code would have required that one of those vents was 3 inch all the way from below..
worded as 'one full size stack'..
|
Post Reply
|
Author:
North Carolina Plumber (NC)
Here in NC, they all could tie together and still go out with 2" pipe. The vent only has to be half the size of the building drain.
|
Post Reply
|
Author:
hj (AZ)
Half the pipe size, or half the pipe area? A big difference.
|
Post Reply
|
Author:
North Carolina Plumber (NC)
Pipe size, 4" building drain = 2" vent. 6" building drain = 3" vent.
|
Post Reply
|
Author:
hj (AZ)
Where I have been it has ALWAYS been about area, and 2" pipe is ONE-FOURTH the size of a 4" one, so it takes TWO 2" vents to equal a 4" drain.
|
Post Reply
|
Author:
apcalabama (AL)
It is perfectly legal to combine your vents. This is called stack venting or buoyancy vent.Lower air pressure in any structure will always equialize through proper sized vents.Always be sure you have your san_T facing the right direction due to flow direction if stackventing.
|
Post Reply
|
Author:
hj (AZ)
quote; facing the right direction due to flow direction if stackventing.
That is an "inspector requirement" and has absolutely NOTHING to do with the flow of a gas, which is what air is.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: