Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
roundrightfarm (WV)
I've got a bathroom and kitchen that share a wall. This wall contains the vent to the toilet as well as the sink drain. The top of the toilet bowl is 16 1/8" from the floor and I'm assuming this is the flood rim. I want to stub out the sink trap arm at 16" above the floor to accommodate a deep sink. Does this violate the rule that says a vent (the toilets) should be vertical, or at least not less that 45deg, until it is at least 6" above the fixtures flood height? The sinks trap arm is horizontal below this height.
Thanks
|
Post Reply
|
Author:
packy (MA)
if your code allows wet venting a toilet with a kitchen sink then you are OK. rough the sanitary tee for the kitchen lower than 16 if you are going to have a disposer with the deep sink. 14-14 1/2 would be more like it.
as for the horizontal pipe, that is not a part of the wet vent.
|
Post Reply
|
Author:
roundrightfarm (WV)
Thanks Packy,
We are in a rural area that does not have plumbing inspections. Still, I like to pay attention to the codes for my own sake. Do some codes not allow went venting a toilet with a kitchen sink drain? If so, what is the reasoning behind it?
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
my mistake.. i was thinking of a washing machine. they are not allowed to wet vent another fixture (MA code).
too many suds.. other than that wet venting is the prefered method of venting. the vent is washed by the wet venting fixture. if the vent gets blocked, you will know right away as the sink will not drain..
|
Post Reply
|
Author:
hj (AZ)
Some do not, the thinking being that the flow from a garbage disposer, for example, could induce a negative pressure in the toilet.
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|