Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
poissonn (Non-US)
Hello All,
I've asked a local plumber to give me some advices on how to relocate the components of my bathroom on the first floor of my single story house (bathtub, toilet) as well as the main stack in a wall. I felt I needed to check with other people to make sure everything's all right before I start putting everything together. That's what we came up with:
The main drain used to go from the basement all the way to the roof in straight line. Now, as you can see, I have about a 4 feet offset to get it inside the wall on the left of the picture. The piping runs either parrallel with the 2x8 floor joists or underneath. Anything wrong with this diagram?
Thanks a bunch.
|
Post Reply
|
Author:
packy (MA)
i would run the tub into the end of the 'y' and roll up the side of the 'y' with a street 45 in it to accept the lav.
i don't see any cleanouts..
|
Post Reply
|
Author:
poissonn (Non-US)
Good idea about the tub and lav, haven't thought of that. Do I need more than one cleanout? Where would be the best spot? I did not put one as there was none currently with the old piping routing.
|
Post Reply
|
Author:
North Carolina Plumber (NC)
That 4 X 3 spigot bend needs to enter the vertical pipe with a tee, not a wye and 45. I see it's labeled both ways.
Personally I'd leave the tub wye and lavatory drain as is, although it'll work fine and pass inspection either way.
I'd use a 2" cleanout tee just below the tee for the sink drain.
|
Post Reply
|
Author:
poissonn (Non-US)
Yeah, wasn't sure about how to enter the 3" vertical pipe with the water closet, I'll use the san-tee as per your recommendation! I added the 2" cleanout also. Is there a minimum length I need to have between the san-tee of the spigot bend and the elbow underneath that offsets the drain?
As for the lav and bathtub junction, if both are good, I'll see what fits best in the ceiling. Again, thanks a lot for your answers, they are very valuable
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
my code says a cleanout is needed at the base of every stack.
so, where the toilet goes into what you have marked as a s-tee and down lower where it says 3 inch main drain to basement would be considered 'base of a stack'..
|
Post Reply
|
Author:
poissonn (Non-US)
Good to know, i'd have to check in the canadian's code what are the requirements, but I guess I'll install some...better safe than sorry!
|
Post Reply
|
Author:
packy (MA)
as far as i am concerned... you can never have enough cleanouts or enough shutoffs.
|
Post Reply
|
Author:
exapprentice30 (MA)
You may want to consider increasing the vent to 4" in the attic below the roof to prevent frost closure if you have very cold winters.
|
Post Reply
|
Author:
poissonn (Non-US)
I will! Actually I think the part going outside in the roof is already a 4in stack,
Is there a minimum distance i need to keep between the san-tee of the 4x3 spigot bend and the 90 elbow below that is going horizontal?
I swear I read something about that somewhere but I can't find it anymore...
|
Post Reply
|
Author:
exapprentice30 (MA)
I'm not sure what your code says. I have seen several smaller vents frost over from the moist air in the pipe. In my state on 3" horizontal pipe not exceeding 1/4 inch per foot pitch the vent can be 8ft from trap to the vent and 10ft on 4inch.
'
'
Edited 2 times.
|
Post Reply
|
Author:
sum (FL)
not a plumber just a DIYer.
Quote
The piping runs either parallel with the 2x8 floor joists or underneath.
Does it mean if you run it underneath, you have more freedom with the layout of the pipes? Seems if you run it underneath it will be more excavating but you avoid some elbows. For example the 3" toilet line can run at whatever angle it needs to go directly into a sanitary tee, and not through a long sweep 90, and you probably avoid having to drill big holes in your floor joists...2X8 is only 7.25" deep, and a 3" pipe OD is 3.5", thats taking out half of it.
|
Post Reply
|
Author:
poissonn (Non-US)
Actually, I can only run underneath in the bathtub area. Where there is the pipe from the spigot bend to the wall, I run parrallel with the floor joists, than I make a turn and run behind the wall in the basement, that's why I need those bend. Wish I could do it some other way, but I prefer to keep headroom downstairs and not make swisscheese out of my joists!
Edited 1 times.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|