Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
John2.0 (IA)
We have back-to-back 1/2 baths in our building at work. We'd like to make one of them a Washer/Dryer room while adding a shower and moving the toilet in the other one. Is this layout acceptable??
Also, the new toilet drain cannot simply go "south" and connect to the main; due to obstructions it must head toward the old toilet area as shown.
|
Post Reply
|
Author:
packy (MA)
it looks OK to me. can you tie the new laundry into the existing main stack? this will wash the base of the stack clean as it drains and no vent needed as it will be stack vented.
also, if done correctly and within the proper distance, the new toilet is stack vented. it then will not need a seperate vent.
|
Post Reply
|
Author:
John2.0 (IA)
Unfortunately I cannot tie the washer into the main stack. It's encased in a block wall and there are other obstructions. The toilet will be about 5 ft from the stack but I'm told its always a good idea to vent the toilet, especially if you're already tearing up the floor to put in the drain.
|
Post Reply
|
Author:
packy (MA)
plan-B
eliminate the toilet vent. use a 3 inch "Y" for the washer drain connection. come out of the floor 3 inch and put a 3 x 2 x 2 sanitary tee for the washer drain and vent. the 2 inch washer vent connected to a 3 inch drain will be more than enough air for the toilet/washer wet vent.
|
Post Reply
|
Author:
John2.0 (IA)
I LIKE IT!! Thanks, man!
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
The washer connecting downstream of the toilet with a "Y" could aspirate the air and suck the water out of the toilet. Put the toilet vent in.
|
Post Reply
|
Author:
packy (MA)
it would be a cold day in phoenix when a washer drain hose with a 3/4 inch opening draining into a 2 inch pipe that dumps into 3 x 2 x 2 san tee would aspirate a toilet. also there is a main stack at the end of the run.
in new england slang.. it ain't gonna happen..
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor: