Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
hilltop (PA)
I live in a mobile home park any they are shutting off the water to work in the lines. It is siphoning my tank and causing my elements to burn up. Why is this happening and how do I keep it from happening again?
|
Post Reply
|
Author:
m & m (MD)
Your cold water supply to the house should have a check valve in it. Either yours has failed or you do not have one.
|
Post Reply
|
Author:
hj (AZ)
The only way it could happen is if you have a leaking hot water faucet. There is normally a "hole" in the cold water line, inside the tank, to break the siphon as soon as the water level drops, does your cold water go into the bottom of the tank? Either install a vacuum relief valve on the tank's cold water line, (the best solution), or install a check valve and hope it seals completely.
|
Post Reply
|
Author:
m & m (MD)
Many mobile home WH's are cold fed at the bottom of the tank.
|
Post Reply
|
Author:
hj (AZ)
I don't know about "many" but I have only seen a few like that.
|
Post Reply
|
Author:
hilltop (PA)
Thank you. My tank is fed from the bottom. How would I know if the cold line has a hole when it's inside the tank? I don't know what a check valve is. Also I don't have any leaking faucets but what if there is a leak where I can't see or get to it?
Edited 1 times.
|
Post Reply
|
Author:
hj (AZ)
The "hole" is only on heaters that have the cold water into the top. A bottom feed tank needs a check valve, which any plumber can obtain and install. he can also determine WHY the negative pressure in the tank did not keep the water in the tank.
|
Post Reply
|
Author:
hilltop (PA)
Thank you...I'll look into it today...appreciate the input.
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
a check valve on the cold side of a water heater will mean an expansion tank must be added.
simpler to bring the cold 6 inches higher than the tank and install a tee with a watts N36 vacuum breaker.
|
Post Reply
|
Author:
bernabeu (SC)
packy is absolutely correct
for the OP:
loop the incoming cold water above the tank, install a vacuum breaker at the top of said loop, then drop down and connect to inlet of tank
watts water heater vacuum breaker (install on top of supply loop, NOT on heater)
the vacuum breaker will 'open' to admit air to break the siphon if or when the cold water supply pipe 'back siphons'
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
Edited 1 times.
|
Post Reply
|
Author:
packy (MA)
bernabeu, even a stopped clock is correct twice a day..
my code mandates that the cold pipe rise to 6 inches above the heater. at that point they want a vacuum relief and the cold water shut off.
|
Post Reply
|
Author:
bernabeu (SC)
once a day if a 24hr clock
==============================================
"Measure Twice & Cut Once" - Retired U.A. Local 1 & 638
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|