Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:
Author:
jjsusa (IL)
Hello:
I want to install a water powered backup sump pump in my home. I live in the western suburbs of Chicago, IL. I realize I need a backflow prevention device, but I am confused as to what type. Reading SECTION 890.1130 PROTECTION OF POTABLE WATER (ftp://www.ilga.gov/JCAR/AdminCode/077/077008900I11300R.html), section f1 says I can use either a dual or double check valve assembly if the inlet is connected to a low hazard substance. Section f2 indicates I require a RPZ device for inlets connected to high hazard substances. Is storm water considered a low or high hazard substance? Section g2 concerning installation says I need shut-off valves at the inlet and outlet. Do these valves have to be built-in (like they are for double check valve assemblies), or can install separate shut-off valves. If the former, this seems to contradict the use of dual check valves mention in section f1. I am an educated DIYer trying to do the right thing and learn something in the process. Any help would be much appreciated!
|
Post Reply
|
Author:
packy (MA)
in MA, when we install a heating boiler we are required to use a simple double check valve such as a watts 9D..
if we add non-toxic boiler antifreeze to the system we are required to use an RPZ device. they come assembled with shutoff on each end. so, they consider non-toxic antifreeze to be high hazard.
i'm gonna guess ground water is low level but you better ask...
|
Post Reply
|
Author:
m & m (MD)
The Liberty SumpJet comes with its own backflow device. It is a dual check.
|
Post Reply
|
Please note:
- Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
- Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
- Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
- Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.
Search for plumbing parts on our sponsor's site:
Special thanks to our sponsor:
|