Plumbing education, information, advice, help and suggestions are provided by some of the most experienced plumbers who wish to "give back" to society. Since 1996 we have been the best online (strictly) PLUMBING advice site. If you have questions about plumbing, toilets, sinks, faucets, drains, sewers, water filters, venting, water heating, showers, pumps, and other strictly PLUMBING related issues then you've come to the right place. Please refrain from asking or discussing legal questions, or pricing, or where to purchase products, or any business issues, or for contractor referrals, or any other questions or issues not specifically related to plumbing. Keep all posts positive and absolutely no advertising. Our site is completely free, without ads or pop-ups and we don't tract you. We absolutely do not sell your personal information. We are made possible by:  

Post New
Search
Log In
How to Show Images
Newest Subjects
 insufficient hotwater
Author: Mr.bill (NY)

Have a gas fired indirect system. Was working fine until about 1month ago. Hotwater temperature is not being maintained when heating goes down for night or long periods where heat is not required. Have to run water for several showers or baths to heat up to temperature. Priority switch is on! Circulator is good. technician turned up the low limit temp on the aquastat to no avail(gave a good tip too!). 4 zones each with its own circulator pump. Is there something I am missing? Thank you.

Post Reply

 Re: insufficient hotwater
Author: North Carolina Plumber (NC)

What temperature does the oiler get down to before it fires ?
Does the indirect heater have it's own circulator pump or does it use a zone valve ?

Post Reply

 Re: insufficient hotwater
Author: Mr.bill (NY)

it has its own circulator pump

Post Reply

 Re: insufficient hotwater
Author: Mr.bill (NY)

water is luke warm. Well below the low setting on aquastat.



Edited 1 times.

Post Reply

 Re: insufficient hotwater
Author: North Carolina Plumber (NC)

Either the pump is not running or the boiler temp is too low.

Post Reply

 Thank you I will check it right away! cool
Author: Mr.bill (NY)

Thank you I will check it right away!Boiler is firing at 180 degrees.



Edited 2 times.

Post Reply

 Re: insufficient hotwater
Author: packy (MA)

pull the sensing bulb out of the thermometer well. stick it in cold wter to see of it is calling the control to heat?

Post Reply

 Re: insufficient hotwater
Author: Mr.bill (NY)

Replaced thermostat on Weil McClain Gold plus30 storage tank.Drywell for sensor was dry when removing old sensor. Removal was smooth no buildup of corrosion in tube, No change to problem, Water still cools down during overnight. Taco control box priority switch is on and confirmed wiring to water tank thermostat. Has anyone experienced trouble with controls? Control box is working fine for three heating zones.

Post Reply





Please note:
  • Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.
  • Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.
  • Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.
  • Plbg.com is also not a place to ask radiant heating (try HeatingHelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Search for plumbing parts on our sponsor's site:




Special thanks to our sponsor:
PlumbingSupply.com


Copyright© 2024 Plbg.com. All Rights Reserved.